Hayward heat pump

Brian Jones

Member
Sep 13, 2020
10
Nashville
Pool Size
14700
Surface
Vinyl
Chlorine
Salt Water Generator
SWG Type
Pentair Intellichlor IC-40
I have HEATPRO 110K AHRI HP21104T,
Two years old. It turns on, then right off before hitting set temp. No error code. Water flow is fine. Condensation line is not clogged. The problem is this is not consistent. Almost seems it happens when it is very humid. But not sure. Hayward has no service reps in my area. No HVAC companies want to check it. Im at a loss at what to do. Any similar experience?
 
First thing to check is the refrigerant pressures. For that you need the gauges HVAC techs use. And if you are low in refrigerant you need an EPA certificate to purchase it.

Keep on asking around to find someone with HVAC tools who will take a look at your unit after hours. Or find a retired HVAC tech.

I would get more noisy with Hayward to support what they sell.
 
May be a question of semantics. Does it turn off right after starting (short cycling) or off before it reaches the set temperature? This should be the installation guide for your unit https://hayward-pool-assets.com/ass...s/HeatPro-Installation-HP2xxxxT-HP2xxxxBT.pdf This should be the owners manual https://hayward-pool-assets.com/ass...manuals/HeatPro-Owners-HP2xxxxT-HP2xxxxBT.pdf I am a little confused by the wiring diagram in the installation guide as HT is listed as high temperature switch but seems to be jumpered on the board and WTS (water temperature sensor?) is not listed at all and is connected to "sensor" on the board (assume that it is the water sensor that controls the cutoff point after the water temperature reaches the set point.
 
Thread Status
Hello , This thread has been inactive for over 60 days. New postings here are unlikely to be seen or responded to by other members. For better visibility, consider Starting A New Thread.