You can find #8 gauge bare copper wire at Lowe's (by the foot)
Then get a copper split bolt (they have those also) to join the two wires together.
Make sure you clean the old wire end to shiny new copper AND the inside of the bonding lug on the pump motor - can you post a photo of it?
before attaching the extension to ensure a good clean connection.
This you can do, but definitely get the electrician to check everything out.
You could have some current leakage, but it could also just be ground potential.
Once you make sure the light niche is bonded and hook up the loop to the pump hopefully you'll see the current go to zero (or essentially zero). If the niches aren't bonded you can add a water bond and that'll take care of it.
I retested after I installed the grounding wire to the pump (as described above), but not immediately before, so I don't know if that is what made the difference in the numbers between this morning and now. When I tested on the 2000m it was 212 and on the 20 it was .2 That number is different from what I got this morning.Do the DC voltage tests on 20, not where you have it set.
Do you have a link to that post so that I can read through that information?In pool bonding that kind of problem is still possible to have. The breakers off don't always result in the problem going away.
Most often in those cases, it is an issue with the power company. The source of the problem could even be emanating from a neighbor's property.
I know of at least one other tfp person that had this issue too.
Thank you. I read through the article. The furthest point from my equipment is going to be around 80 feet. I did just happen to buy 128 feet of 6-3 UF wire for my shop, I can probably use one of the three for the test.This article may help you test your bonding grid. Note it says an analog multimeter is required.
![]()
How to Test a Swimming Pool Bonding Grid
As electrical-related pool accidents spike, it's imperative that pool pros check the safety of their pool wiring. Here's a simple way to do so.aquamagazine.com
The bonding wire reads .19 and sometimes .2.Disconnect the bond wire from the pump and put one multimeter lead on the bond wire and one lead on the pump bond lug and check for ac and dc voltage.
Then, reconnect the bond wire to the pump.
What do all of the wires in the junction box go to?
The volage is DC. And there is another junction box at the other end of the pool.Is the voltage ac or dc?
You're right. I didn't realize that was black tape until I looked at the photo closely then went back to the box and confirmed that is a ground wire.I suspect as you do, that the third conduit goes to the other light.
Looks like you have a ground wire from the power panel, one going to the light through the center hole, one to the light attached to the third conduit, and then the one with black tape looks to be the bond wire from the center conduit.
What I don't see is a separate bond wire going to the junction box, but it could be on the bottom of the box and hidden from view.
Ah. Ok, thank you. I looked at the example and did more reading. Now I understand that the bolt I am seeing at the top is to hold the railing in place and I cannot see a potential bonding wire below the surface, as you described. The pool was built in 2008, would having the bond wire on the aluminum cup explain why it is so corroded now? I mean I can pick pieces out with my fingernail. The pool guy loves to blame salt for corroding everything (because he hates salt pools, our salt cell was put in by a different person), and I was thinking the same thing until you brought that up.Quaker Plastics 4 In. aluminum deck anchor - H10010 - INYOPools.com
H10010 - 4 In. aluminum deck anchorwww.inyopools.com
See an example of an aluminum cup anchor here.
The bond wire is below the surface on the screw on the side of the cup.
Note: Aluminum should never be put on a bond wire because it becomes a sacrificial anode to everything else on the bonding grid, and the aluminum will corrode at an accelerated rate.
Only brass or other corrosion resistant materials should be used for anchor cups.
Here is an update. I called the pool guy and left a message asking about the bonding. He did call back and said that he did a 6x6x6 so 6"×6" grid with #6 wire and connected all the pool parts to it. He said the lights have a ground with a nut inside and outside the niche (not sure if I am saying that right). But I do not know how the lights are tied to the equipotential grid. Obviously I have some sort of issue with it not being connected an am going to try this suggestion from earlier.Aluminum will corrode in any case. Being on a bond wire can accelerate the corrosion.
Stray voltages and currents can be extremely difficult to diagnose and fix.
Maybe contact a pool builder and ask for a referral to an electrician who does pool bonding and electrical.
This article may help you test your bonding grid. Note it says an analog multimeter is required.
![]()
How to Test a Swimming Pool Bonding Grid
As electrical-related pool accidents spike, it's imperative that pool pros check the safety of their pool wiring. Here's a simple way to do so.aquamagazine.com
Do you have a link to that post so that I can read through that information?