It feeds the pool pump. 1 hp. Lights are on different line with GFCIWhat does the breaker feed?
Your current breaker is two 120V breakers ganged together for a 240V circuit.
If you put in a GFCI CB it needs to be a single 240V GFCI to work properly.
Thanks Allen…Yes, NEC requires pool pumps to be on a GFCI CB.
Electrical GFCI - Further Reading
www.troublefreepool.com
I have one more question….If I pull the two gaged 110’s out too put the single 220 in…what about the other pole… It’s not part of the equation any longer?
I’ve replaced many 110 cb’s that you just pull the old one out and put the new one in, but never installed a 220 that I would have to wire anything up. Is it pretty straight forward?What "other pole"?
Each 110V CB has one hot wire connected to each.
A 240V CB has the two hot wires connected to it and a GFCI CB has a neutral wire you connect to the neutral bar.
I’ve replaced many 110 cb’s that you just pull the old one out and put the new one in, but never installed a 220 that I would have to wire anything up. Is it pretty straight forward?
ThanksYup, you pull the two 120V CBs out and snap one 220V CB in. Connect the two hot wires to the CB and connect the neutral wire to the neutral bar.
Note that the 240V CB will have a neutral screw connection that you don't connect to.
I thought it’s 240 because it’s two 110’s together. I was hoping I could remove the 110’s and push the 240 GFCI in. I’m still a little confused about hooking it up though.First, the real question is: "How is your pump supposed to be wired?" Some are wired 120V and others are wired 240V. Some pumps have an option, but most VSP are wired to 1 DP GFCI 20amp CB wired for 240.
Next, your signature says you have a 1HP Pentair pump [Pentair SuperFlo Standard Efficiency Pool Pump | 115-230V 1HP | EC-348190. This can be wired either way. But if it's wired w 2 120 single pole CB's and you want to go GFCI 240, then it's a single DP 20amp GFCI CB...the conductors will be the same, which should be 12ga
If you look, a double-pole circuit breaker is, essentially, two breakers attached to each other, on opposite legs of the power, and the levers ganged so that if one leg trips, the other will also (in theory, doesn't always happen). A double-pole (240v) GFCB is the same with the ground-fault protection built in and both sides will always trip (some only have a single lever). Be sure to hook the neutral terminal on the GFCB to the neutral in your panel for it to work properly. A 240v pump will not have a neutral, but that line needs to be attached.I have one more question….If I pull the two gaged 110’s out too put the single 220 in…what about the other pole… It’s not part of the equation any longer?
Thanks…always want to make sure I’m doing everything correct when messing with electrical stuff.If you look, a double-pole circuit breaker is, essentially, two breakers attached to each other, on opposite legs of the power, and the levers ganged so that if one leg trips, the other will also (in theory, doesn't always happen). A double-pole (240v) GFCB is the same with the ground-fault protection built in and both sides will always trip (some only have a single lever). Be sure to hook the neutral terminal on the GFCB to the neutral in your panel for it to work properly. A 240v pump will not have a neutral, but that line needs to be attached.