That is a great way STOP any work being done in its tracks. -Yes, I am an evil lawyer.Be insistent, maybe mention the word 'lawyer'.
That is a great way STOP any work being done in its tracks. -Yes, I am an evil lawyer.Be insistent, maybe mention the word 'lawyer'.
I was wondering if a letter from his attorney to all the utilities would get their 'A teams' out to the property. What do you think?That is a great way STOP any work being done in its tracks. -Yes, I am an evil lawyer.![]()
OofThe freaking junction box is located under my driveway. They are knocking on everyone's door to see if they can turn off the power and pull meters then working on the main bus.
Probably not. It would be sent to their counsel who would tell them to stop work/communication and then would sit on it for a month or longer. Lawyers slow EVERYTHING down.I was wondering if a letter from his attorney to all the utilities would get their 'A teams' out to the property. What do you think?
Exactly what I said to myself.
A foreman came into a room an apprentice and I were working. Clapped his hands loudly and proclaimed "we need to step it up in here."Probably not. It would be sent to their counsel who would tell them to stop work/communication and then would sit on it for a month or longer. Lawyers slow EVERYTHING down.
Maybe the construction that was recently done on the highway, or the neighbors on the other street behind my house? Hopefully engineering will be able to get into the thick of it.Note that you don't have to have power lines traversing your yard for the yard to be energized. If the neighbor's yard is energized, there is a good chance yours will be as well. Any exposed AC power line underground nearby will generate current to each house via the earth ground to the neutral. The voltage level will be dependent on the distance from the voltage source to each houses ground point much like a voltage divider. You may be getting only 2v because you are some distance from the actual source of the problem.
Yes, they were.Were both of your next door neighbors two of the four houses that had the meters pulled?
Yes, as long as there isn't another grounding rod between the source and your grounding rod. The probability of location gets higher the further away from a grounding rod you get. And by grounding rod, I mean a grounding rod that is connected to mains neutral.Maybe the construction that was recently done on the highway, or the neighbors on the other street behind my house?
Did they shut off all power going out of the transformer?Including my house, 4 homes are on the transformer across the street. They removed each house meter, solar off, turned off the house from the transformer.... 40mV on neutral and nothing on common.
Going in that direction leads to the retention pond and to the highway.Yes, as long as there isn't another grounding rod between the source and your grounding rod. The probability of location gets higher the further away from a grounding rod you get. And by grounding rod, I mean a grounding rod that is connected to mains neutral.
So if you drew a line from your grounding rod to the pool's railing and extended it forward, it is likely to be in that direction away from the grounding rod. Of course, it could also be at an angle off that line but probably not more than 90 degrees.
Yes, they turn off the 4 houses from that transformer. It's possible that it's leaking because it we'll need to see what engineering says.Did they shut off all power going out of the transformer?
Maybe the lines going into the transformer are leaking?
Did you map out the yard for voltage differences?
Yup, corrosion. With tons of water over the years going into the anchors, and not draining quickly (I'm assuming by the looks of it) is this a common issue? I'll take pictures tonight and post them.Like corrosion gone? how much of it is gone?
The light still looks new, with no corrosion.I am actually thinking it is electrolytic corrosion from the offending voltage causing it.. I have seen ladders on here after 10 years and asking about rust specs and not completely rusted out... I am almost 100% sure this has been asked but we are up to 23 pages, Do your lights (if you have lights) look shiny still or do they look rusted and dingy looking?
I knew you had mentioned this previously, and that's what I suspected as well; I just wanted to double-check because they are worse than the shallow end anchors. I have a feeling this stray voltage has been here for some time.The anchors are aluminum, so they will essentially be a sacrificial anode for everything else on the bonding grid.
The stray current is probably causing accelerated corrosion.