My soul is getting crushed
Received my Fenwal in the mail today and it didn't resolve the problem. It was however necessary to replace, since I could never previously get 120V at both F1 and F2 to power the other 120V leg of the 240VAC blower. NOW F1 and F2 to ground BOTH test 120V so I'd say the Fenwal relay is closing and power is flowing properly here. BUT the blower still isn't coming on. I'm also getting 120V between every wire and ground now at the blower connector including red and black, where previously either red or black (can't recall which but one is switched from the Fenwal) was dead.
Barring some type of relay/switch/limit failure, it just has to the blower itself, internal motor wiring, or the motor capacitor - right? The safety switches seem like they'd wait for the blower, and being on the low voltage side and working before the incident i doubt they cooked. The blower DID run on the bench at 120VAC so I'm puzzled, but perhaps that means one winding is dead and not another or something or I wired it so wrong started and shouldn't have
. I checked the blower motor for a short to ground with the power off and verified no continuity (open) from each color to ground. It's sounding like I need to replace this blower motor or capacitor but I hate to spend the bucks and have another heartbreak!

Barring some type of relay/switch/limit failure, it just has to the blower itself, internal motor wiring, or the motor capacitor - right? The safety switches seem like they'd wait for the blower, and being on the low voltage side and working before the incident i doubt they cooked. The blower DID run on the bench at 120VAC so I'm puzzled, but perhaps that means one winding is dead and not another or something or I wired it so wrong started and shouldn't have