Connect Fireman Switch to Jandy JXi Heater
KeithSm
2
Brantford, Ontario
Jandy Truclear / Ei
Hello, I have a Jandy JXi Pool Heater and an Intermatic T101R Mechanical Timer. I would like to add a 56T4042A Heater Control/Fireman Switch. Does anyone know where I connect the fireman switch to the heater? Thank you!
Why do you want to use a fireman's switch? They were designed to let a pool heater cool down before the pump shuts off. Your heater has a cool-down cycle built in to its control.
JXI HEATER CONNECTION AT "FIREMAN'S SWITCH"
Pool School
At the JXi Power Interface Board connect one end of two wires to terminals POOL and COMMON (J6).
Connect the other end of these two wires to terminals 1 and 2 of the AquaLink RS Green terminal bar.
Set pool thermostat to maximum (104 F).
Set the JXi to recognize this type of connection by holding down MENU, POOL, and SPA buttons together for 7 to 10 seconds at the JXi's User Interface. Set REMOTE to T-Stat. Press POOL button to exit.
  • 7609-instructions.pdf
Pool School
That works, but you must remember to NOT set the temperature to 104 on the heater unless that is the temp you desire. That connection is for an automation system to have control of the heater on/off. Without that the heater is on its own. That's why I didn't mention it. The OP has a mechanical timer.
Reactions: JamesW
7.2 Connecting to an AquaLink Control.
System or Remote TSTAT (2-Wire Connection).
An interrupt (on/off-type) remote can be connected as a Remote TSTAT to turn the heater on or off but not perform any other function.
When using this type of connection, remember to set the heater control to “POOL” or “SPA” and set the thermostat control to maximum.
NOTE: When a fireman’s switch is being utilized and “hi-lo-com” is selected, the heater will fire automatically when the contacts close even if the user interface on the heater is off.
7.2.1 Install the Remote TSTAT
• Turn off the power to both the pool/spa control system and the heater unit.
• Follow service access instructions from Section 6.1, Service Access.
• Run the wires from the pool/spa control system through the low voltage knockout on the right or left hand side of the heater.
• Connect the wiring from the pool/spa control system to the heater remote control terminal.
• Connect the two wires to Pool and Common (not Spa) on the J6 terminal bar.
See Figure 15 item “b”.
• Reinstall panel.
• Restore power to the heater and the pool/spa control system.
NOTE: If you install a time clock to control the filter pump operation, it is recommended that the time clock have its own low voltage (Fireman’s) switch to turn off the heater before turning off the pump.
The switch should shut off the heater about 15 minutes before the filter pump shuts off.
This will allow for a more efficient operation by removing any residual heat contained in the heat exchanger back to the pool.