Thanks Matt I did not know that most 2-speeds didn't have on-board timers. How do their owners tell the pump when to run at low vs high speed?
The speed is switched by energizing one or two legs of the 220V AC input. There are relays and Intermatic mechanical timers (similar to what’s in your box) designed to switch two speed pumps between low and high speed. The pump you have just moves all that circuitry on board.
Using/installing/configuring a current sensing relay is really much easier than it looks. All you would need is current clamp ammeter to read the current draw on one of the hot leads powering the pump when it’s running (no speed, low speed and high speed). Then you’d just set the trip point of the relay to a setting between the standby current and the low speed current. Any electrician worth his labor rate could easily install something line that. Trick is finding one you trust.