Help me wire my timer please.

JeaniB

Gold Supporter
May 30, 2019
317
Midwest
Pool Size
14680
Surface
Vinyl
Chlorine
Salt Water Generator
SWG Type
CircuPool RJ-45 Plus

Attachments

  • CB762FA5-F67E-42DE-B5CD-F5A42548E06E.jpeg
    CB762FA5-F67E-42DE-B5CD-F5A42548E06E.jpeg
    509.4 KB · Views: 30
The wire gauge will be fine, but you should have another 2 colors. You should have green for ground wiring, green is always and only ground. You should have white for neutral if this is wired 120v or red (or another color that's not white or green) if it is to be wired 240v. Using only one color wire is confusing, non-code, and is dangerous for anyone that may come along after you.
 
You should use individual 12 gauge black red and green wires. Not a 3 wire bundle.

The wire should be THHN or THWN wire and run in a conduit outdoor.

Is the CB GFCI?

What is wrong with your existing wire from the circuit breaker?
 
The wire gauge will be fine, but you should have another 2 colors. You should have green for ground wiring, green is always and only ground. You should have white for neutral if this is wired 120v or red (or another color that's not white of green) if it is to be wired 240v. Using only one color wire is confusing, non-code, and is dangerous for anyone that may come along after you.
Hmmm,.. the inside looks like 3,..it’s 120v.C2900588-B20F-486D-8471-9795BA3A939C.jpeg
 
You should use individual 12 gauge black red and green wires. Not a 3 wire bundle.

The wire should be THHN or THWN wire and run in a conduit outdoor.

Is the CB GFCI?

What is wrong with your existing wire from the circuit breaker?
The CB is GFCI.
I was afraid the original wire from the CB is what caused the fire this morning??
 
Are you wiring a 120V pump or a 240V pump?
 
I’m trying to get an electrician, since I obviously didn’t do something right,. So far everyone says “ I don’t do pools”😩
 

Enjoying this content?

Support TFP with a donation.

Give Support
I was afraid the original wire from the CB is what caused the fire this morning??

I doubt it was the wire unless the wrong gauge wire was used.

From the little I can see of the wiring I think the wiring was done improperly.
 
Hhhmmmm,.. I’m not sure how to proceed. Everything ran smoothly all last summer,. And until today this season. I’m not sure how to diagnose the problem.
 
That is a 3-wire extension cord, without the ends, essentially. I see it on a lot of above-ground installations. It works but is not ideal. Individual conductors in conduit is best.

If it is going to a single breaker, then, yes it is most likely 120v. A double breaker would be 240v, but I never just guess when working with electricity. Even this, found at Harbor Freight, would take the guess-work out of the problem. For less than $10.00 its well worth it to find out. 7 Function Digital Multimeter

If you are not sure how to use it, read the instructions then practice on an electrical outlet in your home. Open electrical panels can be dangerous and it is better to have the work done by a pro,
 
Ok,.. I’m going to start with ordering a new timer so it will get here. Is there anything wrong with the new timer?
 
None of the wire to your smoked timer or the cable spool you have looks like it is outdoor rated wire.

Solid THWN wire run in conduit or UF rated cable is the proper outdoor wiring.
 