Raypak R406A NG heater.What model heater?
Is the heater controlled by any automation?
The heater ran at some point to melt those pipes.
Here is the wiring. Bottom right wires are the heater, bottom left wires are the pump and far left is the SWG. Everything turns on by the timer. We use the manual switch on the heater to turn it on and off, but it doesn't get power unless the timer is on.The left pipe is the inlet and the right pipe is the outlet.
The left inlet pipe looks more collapsed then the outlet pipe.
If the pipe would have overheated with the pump running the inlet pipe would not overheat and only the outlet pipe would collapse. The heater has a pressure switch. With your pump off the heater can still have pressure in its pipes and allow the heater to run. With no water flowing through it the heater will push hot water into both pipes, heating them until they are pliable and collapse.
Post pics of the timer box wiring and how the pump and heater are controlled by it.
Let's see if @JamesW has other thoughts.
Thanks. I will try to remember to get everyone to do that going forward. Would the temp sensor not cause the heater to stop heating once it reaches 90 and just slowly cool down and on, or does it get that hot sitting there?Good advice posted above. Heated water radiates to both sides of the heater thru convection ive seen this happen before. A good extra step is shutting the gas valve off when not in use if your manually turning heater on and off anyway....your already standing there
It does not have an external bypass and I would say its about 4 feet higher than the pool surface.Does the heater have an external bypass?
What is the heater elevation in relation to the pool?
Can you post more pictures of everything?
I would put a flow switch and not a pressure switch.
I would have a cooldown period of about 5 minutes from heater shutoff until pump shutoff.
I would have a cooldown period of about 5 minutes from heater shutoff until pump shutoff.
The pump is IntelliFlo and it has its own timer, which might be part of the problem.
True but that still puts blame on the pressure sensor switch, correct?The pump is IntelliFlo and it has its own timer, which might be part of the problem.
Probably.True but that still puts blame on the pressure sensor switch, correct?
The usual cause for this is the pressure switch, yes, allowing the heater to continue to fire at low or no waterflow. Try the test MSchutzer described. As they are not expensive I would replace the pressure switch and then do not make any adjustments to it. I have seen people adjust the switch to compensate for the lower waterflow of a VSP and this, too, can cause the problem you see. The internal temperature of the heater in the firebox is right at 2000 degrees according to manufactures. That heat has to go somewhere and good waterflow is the answer or there are problemsTrue but that still puts blame on the pressure sensor switch, correct?