Hi all. I have an iAqualink RS4 system and I was wondering if it's possible to wire a second JVA in parallel with an existing one so they both activate together.
I have a couple instances where I would like to use this:
Close spa footwell return during spa mode / open during pool mode.
Actuator between vacuum and main drain. - Open main drain when water feature JVA opens / close main drain when water feature is off.

Is this possible? I don't need any more separate relays, I'd just want them to activate with existing ones.
 
Welcome to TFP.

Yes, you can wire two actuators in parallel.

According to this thread you may have one oscillating if they are not set to stop in the same positions…


Also each JVA requires .75 amps at 24V AC. Driving more then two actuators can require more power then the iAqualink actuator sockets can deliver.

 