Hey there, I have a current setup of two switches - one for pump and one for heater. Everything’s on 240v. Looking to automate with the WiFi timer and just want to make sure wiring is correct.
System won't work if wired according to your diagram. If you wire it that way your red/black and grey/black will cross-phase (cause a short) and at the very least trip the breaker. More likely it will destroy the device, the wiring, and possibly harm you.Hey there, I have a current setup of two switches - one for pump and one for heater. Everything’s on 240v. Looking to automate with the WiFi timer and just want to make sure wiring is correct.
d,I have a current setup of two switches - one for pump and one for heater. Everything’s on 240v.
Is this a heat pump? You don't need a 40a breaker for a pump and standard heater.Thank you. So I'm assuming then I should replace the breakers with a single 40amp and supply one end to COM1 and the other to COM2?
Without seeing your system its hard to tell, but most standard (non-LoNox, no blower) RayPak pool heaters wired for 240 draw 2 amps max and are wired to the same circuit as the pool pump.From what I know, it’s just a heater. It’s about 2 years old, raypak natural gas. Pool is only open in warmer months.