In electrical, the saying is "The problem lies where the power dies". If you don't have voltage to a motor, you work your way back to the circuit breaker until you get voltage.
The same concept applies to gas. The problem lies where the pressure dies.
Since you're not getting steady pressure when the heater turns on, you have to check before every valve until you get steady pressure.
There's a T near the meter that will give you a good place to check the pressure.
Connect the manometer there and turn the heater on to see if the pressure stays steady or drops off.