Here are some photos and a dropbox link to a video of the cycle. Sorry my voice is a bit muffled. IMG_1240.MP4
I removed the bottom bolt completely while the pump was running. No water at all.Did you actually remove the bottom bolt?
You need to check the gas pressure before firing as as the heater tries to fire.
Yeah I could smell a puff of gas when the main valve opened, and a click (the main valve), but the regulator valve never opened and so it would shut down the gas flow. If its the solenoid, they are easy to test with an ohm meter. just check and see if the coils are shorted to start off with. But I didn't know what I was looking for on mine and I pulled the whole gas valve out and cleaned like I was working on a carburetor. It was after I reassembled it I could see one of the valves wasn't opening.I can smell gas which tells me gas is making it through the valve and out the vent by force of the blower. I can't see how I would be able to smell gas if the valve wasnt opening? Thoughts?
Ahh ok, I'll check that!Yeah I could smell a puff of gas when the main valve opened, and a click (the main valve), but the regulator valve never opened and so it would shut down the gas flow. If its the solenoid, they are easy to test with an ohm meter. just check and see if the coils are shorted to start off with. But I didn't know what I was looking for on mine and I pulled the whole gas valve out and cleaned like I was working on a carburetor. It was after I reassembled it I could see one of the valves wasn't opening.
Through process of elimination I addressed everything but the valve. Sta-Rite tech support stopped short of troubleshooting the gas valve, and the company that makes the valves won't service them..they just tell you to replace it.. so I did what my daddy always said.. "it's already broke, so you won't make it worse by trying to fix it. "
If you open a line a that has no flow and has previously has flow it will still smell like gas. The mercaptans used as odorants are incredibly persistent. Check for flow and pressure to be sure you have gas not just smell.I can smell gas which tells me gas is making it through the valve and out the vent by force of the blower. I can't see how I would be able to smell gas if the valve wasnt opening? Thoughts?
THat's exactly what mine is doing.. Multimeter out! I'll give it a test.Just watched your vid.. that looks eerily similar to my issue. Once the 3 flashes start on the Fenwal there is an ignition lockout and nothing is going to lite. Current to the ignitor is shut off. Eventually the service light would come on and then the heater would power off like a normal shut down (in my case). Also I bet if you turn over the circuit board on the controller there will be no diag lights. Those diag lights will give you an insight into other things that could be causing the ignition lockout. If there are none.. then everything else is likely working as it should.
I see you are correct...musta been someone else that I was helping with a different heaterSwamp,
Thanks for chiming in, I should have called you in as you were so helpful in my previous heater problems. One question when you mention metal screen are you talking about the part inside the flame holder (#11)? Mine did not have this. Only the flame tube and the igniter was in a separate opening beside the flame tube mounted a few inches away in the lid. The more I look at this it definitely looks a lot different from mine. Not sure if this makes any difference in the diagnosis or fix. Just want to learn the max I can from you.
Chris
All values were between 17 and 100 ohms so sounds like valve is good. I will get a manometer I guess is next step to be sure of flow.THat's exactly what mine is doing.. Multimeter out! I'll give it a test.
After the valve clicks I am smelling gas for a brief second. I'll run down a manometer online and rule the supply issue out. I did check all of the solenoids with ohmmeter and they tested under 100 ohms.Sorry I missed the video until just now. You definitely have a gas/air mixture supply problem if you are certain the igniter is heating. Are you not smelling gas in the vent for a brief time during the blower operation? If not, then you have a gas supply problem to the fire box. This is most likely:
There are ways to check for adequate gas and flow without a digital manometer or a home made manometer but they are not safe so I won't go into them. You really need a manometer or a gas plumber. You can easily make one with tubing that I've tested and used myself. Took about an hour to make.
- Supply to the gas valve in the heater.
- Gas valve has an internal obstruction or solenoid is opening but not opening the gas valve.
Chris
I presume you disconnected the leads to the solenoids when you tested it. Yes? James mentioned there are little ports on the side where you can check for gas on the inlet and outlet side. they are little set screws. I never fussed with those but they might give you some insight as to whether gas is making it through the valve.... I pulled my old valve out for reference. I can send you a pic if you want.All values were between 17 and 100 ohms so sounds like valve is good. I will get a manometer I guess is next step to be sure of flow.
Yes please do, I would appreciate it! And yes I removed the leads before testingI presume you disconnected the leads to the solenoids when you tested it. Yes? James mentioned there are little ports on the side where you can check for gas on the inlet and outlet side. they are little set screws. I never fussed with those but they might give you some insight as to whether gas is making it through the valve.... I pulled my old valve out for reference. I can send you a pic if you want.