In the further reading that Allen referenced look for the method to add a ground wire between the burner and the ground wire on the controls panel. Sounds to me that you may have poor ground connections that interferes with flame rectification. This is a fairly common failure in older flame rectification controlled heaters and it's very easy to add the ground wire. The unit detects flame by passing a tiny signal from a flame sense rod (or the igniter itself if you don't have a separate flame sense rod) through to the burner and this must be detected by the ICM in order to open the gas valve. The current that passes is only a few millionths of an amp so it's easily interfered by corrosion anywhere in the ground. If your ICM is a Fenwal do you see a red light that is flashing? How many flashes do you see?
I hope this helps.