NowintersinAZ
Well-known member
- Oct 18, 2020
- 188
- Pool Size
- 7560
- Surface
- Vinyl
- Chlorine
- Salt Water Generator
- SWG Type
- Intex Krystal Clear
See the arrows in the upper left corner? Make sure the set screw in the neutral bar is tight. Then also what should be a green screw on the other end of the bonding jumper attaching it to the metal enclosure. If they are tight then loosen and re-tighten to make sure proper connection is made. You might want to take a voltage reading from one end to the other and see if you get that stray voltage across this point, then perform the tightening. top of set crew to top of other crew.
Lifting that neutral is going to be tough as it's bare and will touching every other bare conductor in the enclosure. It will need isolating in some way.
I see a lot of aluminum wires these can become loosened over time because of expansion and contraction from heat. Every couple of years they should be checked to make sure they are tight. Even the mains coming in.
(disclaimer: My lawyers want to make sure you understand I am not advocating that said owner if not a licensed electrician should attempt to touch or engage with these main wires from the electric meter in any way.) SAFETY FIRST call someone to complete that task please.

Lifting that neutral is going to be tough as it's bare and will touching every other bare conductor in the enclosure. It will need isolating in some way.
I see a lot of aluminum wires these can become loosened over time because of expansion and contraction from heat. Every couple of years they should be checked to make sure they are tight. Even the mains coming in.
(disclaimer: My lawyers want to make sure you understand I am not advocating that said owner if not a licensed electrician should attempt to touch or engage with these main wires from the electric meter in any way.) SAFETY FIRST call someone to complete that task please.

Last edited: