*Shallow end, being shocked when grabbing railing*

Is this the wire going to your ground rod?

Can you have the electrician break this wire and check for voltage between both ends?

Or disconnect at the ground rod and test between the rod and the wire.

Check for voltage, amperage and frequency on the scope.

Reconnect after test.

1627836402654.png
 
With every test with every wire that gets removed you should check the pool. Testing for voltages is good but testing the annoying voltage when a parameter is changed is better.
I agree with you, and will do this from now on.
The water to deck reading is difficult to establish a good deck contact.

You probably need to find a way to make good contact like wetting the deck and then putting a metal plate on the wet deck.
I always measure with the deck wet, and I double check using the deck anchor for the cover.
 
  • Like
Reactions: JamesW
Another white wire used for power.

At least it is taped black on this side.

The other side might not be taped black, which risks someone using it as a neutral.

View attachment 360554
I don't believe there is any way a hot could be hooked to a neutral and still hold. Neutrals are tied to the EGC at the panel and would instantly trip. Also it would make a direct short across the transformer which would also trip the breaker.
 
  • Like
Reactions: JamesW and mas985
t should at least be marked on both ends.
Of course. When I’ve seen it in the past they usually taped the last inch with electrical tape so the end was ‘black’ on both ends. This one evidentally didn’t care.
 
What does this GFCI go to?

Does your PowerBlaster power monitor show you the voltage and current on both legs of the power?

If yes, is the voltage on each leg the same?

View attachment 360552
That GFCI goes out to the pump and the GFCI outlet.
Another white wire used for power.

At least it is taped black on this side.

The other side might not be taped black, which risks someone using it as a neutral.

View attachment 360554
This makes me want to scream because of the all inconsistencies in the panel. Multiple labels are incorrect because of all the additions over the years. I'll need to find out where this goes. 🤬 Thank you @JamesW for seeing this.
 
Last edited:
That GFCI goes out to the pump.
It looks like it has a neutral. What does the neutral go to?
I'll need to find out where this goes.
Most likely, it isn't a problem because it would instantly trip as was pointed out.

In any case, I automatically discount the quality of work when I see things like that.

In my opinion, a good electrician has plenty of wire in all types and colors to do the job correctly.
 
  • Like
Reactions: Newdude
What does this GFCI go to?

Does your PowerBlaster power monitor show you the voltage and current on both legs of the power?

If yes, is the voltage on each leg the same?

View attachment 360552
So this one has the pump and the GFCI outlet outside. The neutral is screwed into the one pole with the Test functionality, and then the second white under it is running to the ground bar.
Another white wire used for power.

At least it is taped black on this side.

The other side might not be taped black, which risks someone using it as a neutral.

View attachment 360554
General contractor BS. This is wired to a secondary HVAC unit. It has more black electrical tape going up the wire apart of the same wire run as the hot.
 

Enjoying this content?

Support TFP with a donation.

Give Support
You work IT right?
Do you fix computers?
troubleshoot networks?
It's the exact same thing!
A process of elimination. Troubleshooting skils are all the same no matter what you're troubleshooting. You may think oh! it's over here only to find it is not. Now you have one less place to look. Go to the next place if it's not there move on and now you know two places it is not.

Take notes record voltages at the pool and at the place you are testing. See a pattern? work on it. Running out of ideas walk around looking over every little detail of the pool and anything electric. When done do it again you may have missed something been thinking of another project and missed it.

Troubleshooting is not always and most times not easy and takes patience and perseverance.
You are correct, the same set of troubleshooting processes needs to be followed with thorough documentation.
 
  • Like
Reactions: NowintersinAZ
In this picture, the bottom breaker is a two-pole 230 breaker and the one above it is a single pole 115 volt breaker.

Does the wire with a red arrow pointing towards it go to the single pole breaker or the double pole breaker?

Does the double pole breaker have both poles being used or just one?

This is wired to a secondary HVAC unit.
The wires look too small for a HVAC unit.

What is the power rating of the HVAC unit?

1627839834600.png
 
So this one has the pump and the GFCI outlet outside. The neutral is screwed into the one pole with the Test functionality, and then the second white under it is running to the ground bar.
You don't normally have 120v outlets on a 240v circuit to a piece of utilization equipment. The pump circuit is sized for the motor and when tossing random outlets into the mix you no longer have control over what runs on that circuit.

That 15 amp breaker looks unused, if it is can you fish another hot and neutral, if it is all in conduit? Never mind about running new wires right now. Are there any other receptacles on that 240v pump circuit. It's just weird to do that.

Have you turned off that pump breaker and tested the receptacles for power?
General contractor BS. This is wired to a secondary HVAC unit. It has more black electrical tape going up the wire apart of the same wire run as the hot.
This is normal IF run in romex. If in conduit then a hot can not be white taped black, it has to be a color.
 
Last edited:
How is it attached ? Or is it even attached ? I’m not seeing screws (which is good). If I saw that one in the field, I’d expect to see it zip tied or taped to the electric conduit.
 
This entire thing looks sketchy.

You have a bunch of loose wires, dirt and corrosion.

It would be interesting to see the voltage and waveform on the scope of the power from the phone company.

Phone wires.jpg
 
This entire thing looks sketchy.

You have a bunch of loose wires, dirt and corrosion.

It would be interesting to see the voltage and waveform on the scope of the power from the phone company.

View attachment 360575
I hooked it up to oscilloscope very quickly, it was intermittent voltage and frequency. Then.... It started to rain 😫
 
This entire thing looks sketchy.
Lol. It’s 40 year old outdoor copper. It should be Statue of Liberty green and look like wire spaghetti from all the times it’s been played with / modified. All things considered it’s not too bad. (Although certainly not ‘neat’ or showing worker pride).
 