Raypak Heater blew it's thermal fuse

meestahmarc

Well-known member
Jun 7, 2018
160
Paramus, NJ
Pool Size
32000
Surface
Plaster
Chlorine
Liquid Chlorine
Hi there, so I have a 10 pack of new fuses ordered and will solder on a new one. Was $6 for the 10 pack. However, I need to figure out why the fuse tripped and I supposedly have flame rollout. I assume my vent is clogged, so my question is how do I clean the exhaust? do I unscrew around the top and try and get the top piece off where there is some debris inside. unit is older r336a model. I've had it 4 years now, been good. I never cleaned it, so this is overdue. thank you
 
I unscrewed 6 screws holding on the lid, took it off and saw a lot of leaves on the exhaust vent... cleaned up. I suspect this was the issue. The thermal fuse detects heat in the bottom chamber of the unit, if temp gets too high in there it blows the switch because it knows something is wrong. I do NOT believe its trying to detect if flames are coming out and on the fuse because the fuse housing is plastic. the rayopak part is like $30 - 40 bucks. I'm planning to just cut off the old fuse and solder on a new one. I bought a 10 pack for $6 on amazon. Cleaning 9r covering my heater will now be a regular maintenance item for me. I had not touched it in 4 years.
 

Attachments

  • PXL_20210716_120355984.jpg
    PXL_20210716_120355984.jpg
    700 KB · Views: 10
  • PXL_20210716_122242970.jpg
    PXL_20210716_122242970.jpg
    600.2 KB · Views: 9
If there was enough of a blockage to cause the rollout switch to melt, I would also check the underside of the heat exchanger from the burner box for sooting,which may also need to be cleaned. If you plan on replacing just the fusible link/ thermal fuse in the existing ceramic housing you need to be sure that the melting point of the replacement is exactly the same as the original. The heater has only been approved with that exact melting point.
 
how do I access the area between the heat exchanger and the flame? yeah, that might be clogged up too. I got 152 degree fuses, I believe that is either exact, but I don't think a few degrees, like +/- 5, will really be too drastic. It's just kills the unit if that general area starts to get really hot. thanks
 
152 degrees C is the correct one. Don't know what your model number your heater is. Usually you would disconnect the gas manifold by disconnecting at the union and remove the burner tray to access the underside of the heat exchanger. Photos of the heater and the front of the heater with the cover off and model number would be helpful.
 
Hi, so I stand corrected. I replaced the fuse and fires the unit back up, it started, so I pulled the cover off and sure enough a flame was still rolling out and firing over the fuse. I guess my unit is still clogged up. I don't quite understand still how to fix it further, so any specific details would help, like exactly where to disconnect.
 

Attachments

  • PXL_20210717_214501489.jpg
    PXL_20210717_214501489.jpg
    425.7 KB · Views: 13
  • PXL_20210717_214456846.jpg
    PXL_20210717_214456846.jpg
    249.6 KB · Views: 13
  • PXL_20210717_221354272.jpg
    PXL_20210717_221354272.jpg
    271.1 KB · Views: 13
  • PXL_20210717_214505462.jpg
    PXL_20210717_214505462.jpg
    295.1 KB · Views: 16
  • PXL_20210717_222113693.jpg
    PXL_20210717_222113693.jpg
    423.1 KB · Views: 19
  • PXL_20210717_222209223.jpg
    PXL_20210717_222209223.jpg
    547.7 KB · Views: 14
  • PXL_20210717_222158434.jpg
    PXL_20210717_222158434.jpg
    541.6 KB · Views: 13
  • PXL_20210717_222226072.jpg
    PXL_20210717_222226072.jpg
    544 KB · Views: 15
  • PXL_20210717_222217059.jpg
    PXL_20210717_222217059.jpg
    601.9 KB · Views: 15
  • PXL_20210717_222416137.jpg
    PXL_20210717_222416137.jpg
    408.6 KB · Views: 12
A few comments about swapping the fuse. It's not that easy, the solder they use to attach it, seems to have a higher melt point than my lead solder, which is like 600 degrees. It looked like a copper solder. I too had to cut off the old leads with clippers. then I scuffed up the tabs with sandpaper and soldered on the new fuse. It's a little tricky and then you need to push it back into the white housing piece.
 
I can see soot under the burners, which makes it very likely that the underside of ther heat exchanger is blocked by soot. In order to possibly give you some directions, I would need you to vacuum out the area below the burners of all debris. Then give me multiple photos showing screws/bolts etc. on both sides of the framework under the burners and a photo of the heater as a whole including the gas piping outside of the heater. We can try to go further from there.
 
It's working!!! I went out to examine the unit again, yes there is a little soot beneath the burners, but not a ton. It seems the burners are held on with 2 bolts on each side and then kept in place by the gas line connection. After some thinking, I decided I'm definitely not going to mess with the gas line to pull out the burners.

So instead I took off the cover again and was looking down above the heat exchange, it didn't seem too dirty below, as best I could see in . I decided to get out my backpack leaf blower and blow down from above. I understood I might actually blow the spot into the holes of the burner, but I decided to take a chance.

After a good blowout... no more flame rollout. There is a small flame below the fuse, but I was able to leave my hand on the fuse and it was not hot at all. Heater worked for the past few hours.

For good measure I will likely buy the OEM thermal fuse from the pool store.

Hopefully this might help someone else in the future and I will be covering my heater in the fall.

Thanks
 

Attachments

  • PXL_20210718_170625564.jpg
    PXL_20210718_170625564.jpg
    522.9 KB · Views: 10
  • PXL_20210718_170629204.jpg
    PXL_20210718_170629204.jpg
    573.8 KB · Views: 9
  • PXL_20210718_171726222.jpg
    PXL_20210718_171726222.jpg
    494.2 KB · Views: 10
  • PXL_20210718_171730098.jpg
    PXL_20210718_171730098.jpg
    389 KB · Views: 10
  • PXL_20210718_171733756.jpg
    PXL_20210718_171733756.jpg
    561.1 KB · Views: 13
  • PXL_20210718_173920329.jpg
    PXL_20210718_173920329.jpg
    509.4 KB · Views: 14
  • PXL_20210718_175010632.jpg
    PXL_20210718_175010632.jpg
    583.2 KB · Views: 12

Enjoying this content?

Support TFP with a donation.

Give Support
Still can't really see everything. You need to kill power to the heater, then shut off gas at the external valve on the right of the heater ( loosen nut on the valve, then turn the tab with the hole in it 90 degrees and retighten nut). Open the union on the gas line that is the first fitting to the left of gas valve ( Use two wrenches so that you don't disturb any of the threaded conections and have to clean and remake the threaded connections). Mark and remove wiring connections at gas valve and also the blue wire going into the burner tray and the green ground wire attached to the burner tray (be sure you know where they go back to, photos before you remove may also help, but mark them anyway). You will need to remove the screw(s) from the blue wire support bracket and the gas valve/manifold support bracket. It looks like the burner assembly is attached by the screws on either side of the burner tray that attach to the inside bottom of the burner tray supports to the bottom of the heater cabinet (remove them). It looks like the pilot tubing may catch on the gas piping to the manifold as you slide the burner tray out. You may be able to bend the tubing slightly to clear the piping as long as you support the riser (vertical part) of the pilot tubing as you are bending it slightly or you could disconnect the pilot tubing at the gas valve. When you reassemble, check all gas fitting connections between the external gas shutoff and the gas valve ( including the external shutoff after you have loosened the nut, turned the tab 90 degrees and retightened the nut) with soap bubble solution to insure that you have no gas leaks (even on the fitting connections that you didn't touch/disturb??).
 
If the latest set of photos is showing how the heater is operating now, you still have a problem. It may be firing, but the yellow flame showing in photo #6 indicates that you still have insufficient air to the burners and are creating both carbon monoxcide and soot. You must have this situation corrected for reasons of safety. If you do not feel that you can correct this yourself, have the heater cleaned and serviced by a qualified company/service technician.
 