The red wire to the pump is on the left terminal which is on the 120v CB and the pump black wire is on the right terminal which is on the other 120v CB.
So the pump and the timer are on two separate circuits.
Except that your CB setup for your pump is not to code and borderline dangerous.
Both CBs must be tied together, like the middle two CBs are, so that when one leg trip the CB, both CBs trip and you don't have either hot wire energized. It is a safety hazard to have it set the way you do. Someone can trip one side of the breaker, see the pump is off, and start working on the pump while the other side is HOT!
In additon you should have a 240V 20 amp GFCI CB for the pump.
The two black wires from the 240v CB go to the timer.
And that powers the Solar controller and will power the SWG. Anything else?
Should the pump be wired to the 240v CB?
The proper fix is:
- Replace the center CB with a 240V GFCI CB made specifically for VS pumps like the Siemans QF220AP or the Pentair PA220GF
- Connect the IntelliFlo pump to the 240V CB
- Change your Solar Controller and SWG to 120V
- Use one of your outside CBs for a 120V circuit to the timer
- You need to chnage the T104 timer with a 240V clock to a T101M timer mechanism with a 120V clock
- Rewire the timer for 120V and connect the Solar Controller and SWG through the timer with 120V
www.troublefreepool.com
I did clean up the wiring (cut ends and re-stripped) on the CB as there were strands hanging and removed the x10 switch and wired in a RF remote for the pool light using the neutral and load from the GFI.
You have those outside CBs providing 240V to the pump and 120V to the lights and solar controller. No wonder things were confusing.
As far as the SWG, the wiring references ground and also that it must be properly grounded and bonded.
Ground and bonding are two separate things.
Electricity and water don't mix. Learn a few basic tips how to keep your family safe when dealing with electricity around your pool.
www.troublefreepool.com
I have located the bare copper ground wire from the pump... that would be the bonding ground to use with the bonding lug on the SWG controller?
It is the bonding wire, not the bonding ground, and you extend it with copper lugs and split bolts to connect to the SWG bond lug.
www.troublefreepool.com
The green ground wire on the SWG power cord would go to the grounding block at the bottom of the wiring box where the green wire from the house wiring is attached?
Yes,
The other two lines on the SWG power cord would go to terminals 2 & 4 on the timer.
Well of you follow the recommendation above you will rewire the timer for 120V and only the hot wire connects through the timer.
Should there be a location where the bonding wire should be attached?
The bonding wire runs from the SWG bonding lug to connect to the bonding wire connected to the pump using copper split bolts.