I have a Pentair Intelliflo3 VSF pump and an EasyTouch Control Panel. In the Auto mode, the pump runs as scheduled from 9:00 am to 3:00 pm every day.
However, everyday I receive an email at 3:05 pm stating that my IntelliFlo/Pro3 VSF is offline.
I would like to be able to start the pump between 7:00 pm and 11:00 to use the jacuzzi but cannot because the controller has lost communication with the pump from 3:00 pm to 9:00 am.
I have read similar posts and tried everything.
How can I correct this issue?
 
Welcome to the forum.

Your pump is wired on the LOAD side of the Filter/Pump relay. It needs to wired to the LINE side, or preferably, directly to its circuit breaker.
 
  • Like
Reactions: Jimrahbe
So today I changed the wiring. You were correct about it being wired on the Load side. I just switched the wires to the Line side.
Power (wires) from the breakers now runs to the Load side and wires from the Line side run to the pump.
However after the schedule ended at 3:00pm, I got the following two error messages:
Pump 1: Communication lost
Chlorinator: Communication lost (I don't have a chlorinator)
I tried to start the pump again but can't.
What should I do next?
 

Enjoying this content?

Support TFP with a donation.

Give Support
HDR definitely needs to be off

There are a couple tricks here:
 
Almost there. Upload them however you did. Then click 'insert' and 'full image' so they aren't grainy attachments at the end if the post.

Screenshot_20240725_204018_Chrome.jpg
 

Enjoying this content?

Support TFP with a donation.

Give Support
Thread Status
Hello , This thread has been inactive for over 60 days. New postings here are unlikely to be seen or responded to by other members. For better visibility, consider Starting A New Thread.