I suspect the problem is your schedule... For the Pump/Filter relay to close, the system has to be in AUTO and the Pool or Spa mode, and the pump needs to be running (or at least supposed to be running..
My guess is you have something like this..
Pool 8 am until 11 am ..... SWCG will be on
Cleaner 11 am until 1 pm .... SWCG will be off
Pool 1 pm until 8 pm ...... SWCG will be on..
You need...
Pool 8 am until 8 pm
Cleaner 11 an until 1 pm
Thanks,
Jim R.