Picked up a RayPak Digital Electronic Natural Gas Pool Heater (400,000 BTU) to replace an old Raypak that was end of life (It was removed before I remembered to write down the model). Pretty straight forward install do to everything lining up easily and I did it myself. It’s been running with water through it for a few weeks and I just got around hooking up the power and gas today. Saw no visible leaks using soapy water or smelled, heard anything.
When I set the gas pilot to On, then turn on the heater and set the temp for the spa to 100 the unit says Spark and I hear it trying to light the pilot light but it never does. It eventual says Ignition Failure; No Pilot Sensed.
I have confirmed gas is flowing at least to the unit. I also can make out a spark, but it never lights.
Is there something I missed in the install? Could it be a case of low pressure? From the gas meter, it is a 1.5 inch metal pipe until it exits next to heater. From the meter to the heater could be 50-60 feet.
Any insight would be wonderful.
Thanks