Searching around, it seems like the issue could be a lot of different things. I'm hoping you guys could point me in the right direction. The warranty expired, so this will be my first attempt at a repair.

Last week, the heater worked fine. Yesterday, it started short cycling. I think it would run for 30-40 minutes and then stop heating. The heater display looked like it normally does when it's on; there was no error code. The intellicenter app made it look like the heater was working, but there was no noise and no heat.

This morning, I went out there hoping to see an error code. I turned it on and it only ran for about 10 minutes, then stopped. The "Service Heater" light is now on if I try to turn on the heater. Still no error code on the display.

The only issue I had to this point was the Stack Flow Sensor had to be replaced about 2 years ago while under warranty. It did something similar (short runs and cut off), but I don't recall if it gave me an error code.

Any guidance on troubleshooting would be appreciated.!
 
Check the thermal regulator.

As a test try and run the heater without the thermal regulator.

Also check the condition of the bypass valve in the manifold.

Does your heater have a 5 button keypad or a 6 button keypad?

 
Ok. Unless you have some quick instructions, I’ll google how to remove thermal regular and bypass valve. I’m usually pretty handy but never touched a pool heater before.

Edit: I replied from my phone initially and didn't see your link. I'll try that. Thanks.
 
Try reading the Installation Manual. It shows where the thermal regulator is. The cap holding it unscrews.

Did you read through the Wiki link above?
 
Check the LED lights on the back of the board and the LED light on the Fenwal module when you get the SERVICE HEATER light.
 
As a test try and run the heater without the thermal regulator.

Also check the condition of the bypass valve in the manifold.
Without the thermal regulator, the heater fired up and almost immediately shut off and lit up the 'Service Heater' light.

I stuck my hand in to feel for the bypass valve. Everything I could reach, felt solid. But this is in a tight and awkward spot so I can't get down there to look in the hole.
 
Check the diagnostic LEDs.


Pentair_MasterTemp_Diagnostic_LEDs.jpg
 

Enjoying this content?

Support TFP with a donation.

Give Support
I finally had a few minutes to take of the panels and trip the heater. It appears my SFS (Stack Flue Sensor) is going off. Is step one to replace the sensor and see if that fixes the problem?
 

Attachments

  • IMG_6313.jpg
    IMG_6313.jpg
    122.9 KB · Views: 1
  • IMG_6317.jpg
    IMG_6317.jpg
    207.4 KB · Views: 1
The sensor is probably doing its job. You may have a broken bypass valve.


While running, press and hold the On button to display the exhaust temperature (Older Models).

The new models use the Menu to get the SFS.

Here is what the normal exhaust temperature should be:
  • Below 250 degrees...very low
  • 250 to 290 ..................low
  • 290 to 350.................acceptable
  • 350 to 480 ..................high
  • Above 480...................error/shutdown.
Note: HD models can be up to 75 degrees higher. HD models use a cupro nickel exchanger, and the efficiency is slightly lower, resulting in less heat transfer and more waste heat.

If the exhaust gas temperature is higher than normal, water may bypass the heat exchanger through a broken bypass valve.
 
This is the Exhaust Temperature I get on my MasterTemp…