With the igniter energized, there will be voltage of 102-132 VAC supplied by the ignition control, test point 13 and test point 10, if the heater is connected to a 120V supply.
If the heater is connected to a 240V supply, there will be voltage of 102-132 VAC supplied by the ignition control, test point 12 and test point 10, with the igniter energized.
This voltage will be applied only during igniter heat up or trial for ignition.
Even if voltage has been confirmed at the end of the safety circuit, the “trial for ignition” sequence is imposed by the ignition control.
This sequence consists of a 15 second period of pre-purge, a 40 second period for heat-up of the igniter and a seven (7) second trial for ignition.
During this last 47 seconds there is voltage between test point 13 and test point 10, or between test point 12 and test point 10.
If satisfactory ignition is not achieved, the igniter is turned off and the system waits for a 15 second inter-purge period.
The system may go through this cycle as many as three (3) times, but thereafter it is “locked out” by the ignition control for a one hour period.
Additional attempts will be made only if the call for heat is interrupted by turning off electrical power or setting the control to “Off” and then back to "Pool" or "Spa" or after the one hour delay.
To trouble shoot the ignition control's igniter, observe that the normal ignition sequence takes place.
After the 15 second pre-purge, note the voltage between test points 13 and 10, or test points 12 and 10.
Then look for the glow of the igniter through the view port on the right side of the combustion chamber.
If the correct voltage is detected between points 13 and 10, or points 12 and 10 during the trial for ignition but the igniter does not glow, check the connections to the igniter.
Check the igniter with the ohmmeter.
Disconnect the IGN120 or IGN240 terminals from the ignition control and the connector at test point 10. Place one lead of the meter on each wire to the igniter.
The resistance should read between 40 and 75 Ohms at ambient air temperature.
If the meter reads outside of this range or shows an open or short circuit, replace the igniter.
If a short circuit is indicated, it is necessary to investigate further to find if the short is from the igniter or the flame sense circuit.
If voltage does not appear between points 13 and 10, or points 12 and 10 during the trial for ignition, there may be a bad connection, faulty transformer, or a short on the ignition control.
Check all connections, the transformer, and the ignition control for loose or corroded connections or failure and replace as necessary.