Hi All - first time posting. I really appreciate all the posts that have helped me over the last few years. I'm posting as I have not seen this problem yet so I've started a new thread. The pool heater was shutting down after a few minutes and restarting and repeating until lockout. Generally no codes, sometimes AFS on the board. All signs pointed to the ground or the igniter flame sensing to the Fenwall. I added the ground under the flame holder and a second above. The problem still persisted. I went to change the igniter and found the area around the igniter cracked and melted. Previously I had cleaned the coils (taking the HX out for full descaling). When doing so I could see the lid was a bit warped so I straightened it and it was flat and no damage around the igniter was seen. That was a few months ago. Now under inspection, I think adding the ground wire, coupled with a missing gasket on the ignitor caused the hot burner gas to escape and melted the lid in that area. Last week I replaced the lid, the two upper insulation pads and the ignitor with OEM parts. The previous hard insulation was in good shape but the soft fiberglass was not around the ignitor hole. Replaced both in hopes it would keep the heat away. All back assembled I smiled and fired it up. First problem. The heater is located in an indoor mechanical room. It filled with smoke and set off the alarms. I shut it all down and figured maybe it's the oil from the manufacturer burning off the new lid. Waited a day and tried again. Less smoke, at first. Then, I looked at the cover where the flame holder gaskets are and saw it warping away from the blower plate. The sheet metal lid was allowing a gap in the gasket and smoky hot air was escaping. I shut it down again as I feel there may be too much heat in the burner or something else that is not good. FWIW I didn't use any RTV on the gaskets. From a design point, it seems the distance between the bolts is too great causing the heat to warp the the lid cover to warp the extent it opened an air gap (< 1/16"). Should I have put RTV around the flange or on the gaskets? Should I be concerned there is too much heat getting to the lid and not use the heater? I did not reinstall the ground wire yet because I wanted the best seal I could get with the new lid. That good seal lasted under a minute until the warping happened. Thoughts?