Heater replacement - advice needed

Is there any downside to getting a heater that's rated too high on BTUs aside from initial purchase cost?

No. You pool will just heat to the set temperature quicker. You use the same amount of gas to heat to a set temperature.
 
  • Like
Reactions: IceShadow
You need to verify that the meter and gas line are big enough for the new heater.
Is it just the pipe size or is there some sort of rate of flow that I need to worry about? I can measure pipe size myself, but I would need an HVAC place to measure rate of flow.
 
Is it just the pipe size or is there some sort of rate of flow that I need to worry about? I can measure pipe size myself, but I would need an HVAC place to measure rate of flow.

It is the meter and any regulator on the gas line that determines your maximum gas service. There may be data plates on your gas meter.
 
The meter should have a label that says how many cubic feet per hour the meter will do.

Usually, the model number will be the cubic feet per hour.

One cubic foot per hour provides 1,000 btu per hour.

So, a 250,000 btu per hour heater will require a 250 cubic foot per hour meter.

The gas line depends on the length and btu/hr required.

What is the distance from the meter to the heater?

What is the current pipe size?

Note that the pipe size is the inside diameter and not the outside.
 
  • Like
Reactions: Arizonarob
The meter should have a label that says how many cubic feet per hour the meter will do.

Usually, the model number will be the cubic feet per hour.

One cubic foot per hour provides 1,000 btu per hour.

So, a 250,000 btu per hour heater will require a 250 cubic foot per hour meter.

The gas line depends on the length and btu/hr required.

What is the distance from the meter to the heater?

What is the current pipe size?

Note that the pipe size is the inside diameter and not the outside.
Meter and heater are close but I don’t know how direct of a run there is. Meter is stamped with 250 CFH so it looks like I should probably stick to my current size of 200k BTU. I can’t tell the inside diameter of the pipe right now. I’ll ask the pool guys when they stop by to troubleshoot it. :)
 
A 200,000 btu/hr heater should have at least 1" gas line up to 100 feet. 1" pipe has an outer diameter of 1.315".

A bigger heater up to 400,000 btu/hr needs at least 1.25" gas pipe up to 100 feet. 1.25" pipe has an outer diameter of 1.660".

You can have the meter replaced if necessary. Sometimes the gas company will do it free. Sometimes they charge.
 

Enjoying this content?

Support TFP with a donation.

Give Support
Thanks for the follow up and glad you're in business again. I'd take it apart as Allen says and blow it out with compressed air or get the service tech out to do it. At end of season a few squirts of bug spray around the base and at pipe/electrical penetrations wouldn't hurt.
 
Thanks for the follow up and glad you're in business again. I'd take it apart as Allen says and blow it out with compressed air or get the service tech out to do it. At end of season a few squirts of bug spray around the base and at pipe/electrical penetrations wouldn't hurt.
I’m still having the guys come by to clean it out. Though when I asked about that they sounded pretty hesitant, like it was a real PITA to take apart. At the very least I’m going to have them check out the controls. The end of last year showed that even all the way down it was still running at 80-85 degrees.
 
they sounded pretty hesitant, like it was a real PITA to take apart
it’s more about how the old parts break while coming apart and won’t go back together. Then it’s blamed on them and not the age of the heater. You might get the disclaimer speech before they touch it. ‘Will be extra careful, no promises,’ etc
 
  • Like
Reactions: markayash
Whelp, the temp outside dropped into the 40s but the pool is now in the 70s. So the heater is certainly working.

I think I'm gonna need to invest in a solar cover...
 