IF code on a 1 year old H250f that ran fine last year. Everything checks out for start up except the gas valve gets 24 volts for about 3 seconds then drops to zero. Is the valve momentary or constantly supplied power while in operation?
Its that "3 seconds" that says one of the boards is bad (Not the display board and both the others need to be replaced at the same time). May still be a warranty. Give it a try.IF code on a 1 year old H250f that ran fine last year. Everything checks out for start up except the gas valve gets 24 volts for about 3 seconds then drops to zero. Is the valve momentary or constantly supplied power while in operation?
This was my thought as well, Ive serviced a bunch of the H series heaters and understand that its a 2 stage valve. After the purge cycle, you hear the first click of the first stage, but never the second where gas actually starts to flow and ignition takes place, its at that point the 24 volts to the valve drops out. This client owns multiple units and Id prefer not to just start throwing parts at it. In my logic wouldnt this all be caused by the ICB?Its that "3 seconds" that says one of the boards is bad (Not the display board and both the others need to be replaced at the same time). May still be a warranty. Give it a try.