Hello all, so my Jacuzzi JSCS40 SWG Power control center burned down a few days ago.
I noticed that the power was off, so I checked and the fuse at the bottom of the unit had tripped so I reset it and turned it on again to see a little puff of smoke come out the back of the unit.
I immediately turned it off and started investigating. The first thing I noticed is that it wasn't grounded! the second thing was that the unit is shipped wired for 220v and the unit was connected to a 120v receptacle. so it must have been under performing this whole time which definitely put some stress on the circuits. LAST but not least! The receptacle is 15A. The power module is rated 2.2A @ 220V and 4.4A @ 120V so if the unit is running while the pump motor is on quick clean mode (RPM = 3450) then the Internal Meter reads 2330 Watts. That means that quick clean mode is already almost 20A so more reasons for it all to fail.
Oh! and of course the receptacle was not even GFCI!! Complete FAIL
Right now I'm looking to replace the Power Module for a Breeze 540 I found on Craigslist but I want to make sure I don't make the same mistakes as my installer, who surprisingly is not replying to my messages.
So first I was going to replace the receptacle and add a WR GFCI 15A. I don't have the money for a full upgrade into 20A right now so I wanted to see if I can make it work with 15A
I lowered the Quick Clean setting on the Pentair VST to 2775 which would keep it around 1000w and therefore 10A.
Then I need to open it and make sure its wired for 120v and last I will install an 8ft grounding rod to ground the unit.
I feel like this would prevent it from happening again! Any thought?
I also bought some S4065K semiconductors to solder back into the faulty unit to see if I can save it!
I noticed that the power was off, so I checked and the fuse at the bottom of the unit had tripped so I reset it and turned it on again to see a little puff of smoke come out the back of the unit.

I immediately turned it off and started investigating. The first thing I noticed is that it wasn't grounded! the second thing was that the unit is shipped wired for 220v and the unit was connected to a 120v receptacle. so it must have been under performing this whole time which definitely put some stress on the circuits. LAST but not least! The receptacle is 15A. The power module is rated 2.2A @ 220V and 4.4A @ 120V so if the unit is running while the pump motor is on quick clean mode (RPM = 3450) then the Internal Meter reads 2330 Watts. That means that quick clean mode is already almost 20A so more reasons for it all to fail.
Oh! and of course the receptacle was not even GFCI!! Complete FAIL
Right now I'm looking to replace the Power Module for a Breeze 540 I found on Craigslist but I want to make sure I don't make the same mistakes as my installer, who surprisingly is not replying to my messages.
So first I was going to replace the receptacle and add a WR GFCI 15A. I don't have the money for a full upgrade into 20A right now so I wanted to see if I can make it work with 15A
I lowered the Quick Clean setting on the Pentair VST to 2775 which would keep it around 1000w and therefore 10A.
Then I need to open it and make sure its wired for 120v and last I will install an 8ft grounding rod to ground the unit.
I feel like this would prevent it from happening again! Any thought?
I also bought some S4065K semiconductors to solder back into the faulty unit to see if I can save it!