Hello,
I'm restoring a heater (as described here) which has been unused long time and while a new parts arrive, I'm testing the rest of the system.
Specifically, I'm testing an actuator valve which is attached to the heater and SPA pump as show the picture below.

Considering the actuator has been unused for a while, I remove it and tested on the lab before connecting it to the Easy Touch.
I applied 24VAC in order to have both directions tested. Specifically, I connect the black wire (in this test I used other colors) with the white wire and the valve rotate in one direction, and connecting the black and red wires, the actuator rotate in the other direction. The stop switch were working as expected as well,

After I connect the valve to the Easy Touch the actuator worked in one direction only.
I measured the voltage on the connector of the motherboard, and the results as below:
During the testing, I didn't install the actuator on the valve (it means, not load).
From a electrical point of view, it seems the MB has an issue regarding the 24VAC mechanical switching but I'm not sure if I'm missing something at firmware/software level that need to be set on the Easy Touch to have the actuator working as expected.
In either case, hardware of firmware, any feedback is appreciated.
Thanks in advance
I'm restoring a heater (as described here) which has been unused long time and while a new parts arrive, I'm testing the rest of the system.
Specifically, I'm testing an actuator valve which is attached to the heater and SPA pump as show the picture below.

Considering the actuator has been unused for a while, I remove it and tested on the lab before connecting it to the Easy Touch.
I applied 24VAC in order to have both directions tested. Specifically, I connect the black wire (in this test I used other colors) with the white wire and the valve rotate in one direction, and connecting the black and red wires, the actuator rotate in the other direction. The stop switch were working as expected as well,

After I connect the valve to the Easy Touch the actuator worked in one direction only.
I measured the voltage on the connector of the motherboard, and the results as below:
- POOL mode
- Black and white: ~29Vac
- Black and red: ~0Vac
- SPA mode
- Black and white: ~0Vac while mode
- Black and red: ~0Vac while mode
During the testing, I didn't install the actuator on the valve (it means, not load).
From a electrical point of view, it seems the MB has an issue regarding the 24VAC mechanical switching but I'm not sure if I'm missing something at firmware/software level that need to be set on the Easy Touch to have the actuator working as expected.
In either case, hardware of firmware, any feedback is appreciated.
Thanks in advance