This is what I was leaning towards. So just to confirm:You may be able to wire the existing 220v GFCI pump breaker to the timer - attach the pump power to the LINE side of the timer and the SWG to the LOAD side of the timer.
Got it. Thank you for helping me understand. The alternative would be to leave the pump power attached as is to the breaker instead of line 1 on the timer. I would still need to supply power to the timer. Is there any advantage to having the pump powered from the breaker directly vs the timer?Nope - the SWG is being controlled thru the timer - that's why you need the ON/OFF clogs for the timer.
- That's a 20 amp breaker. Use 12awg solid conductor wire. Just run over to HD or Lowes and buy a couple feet. Looks like you may need to extend the pump wires as well, so get enough to do that and also a couple of wire nuts to accommodate two 12 gauge wires.
- Yes - you are connecting the wires from the breaker and the pump under the same screws on the timer.
- Yes.
With a T104 timer - lugs 1 and 3 are line - lugs 2 and 4 are load. Notice that the 2 white timer clock motor leads are wired to lugs 1 and 3 so they receive constant power to keep time.
Pop the timer mechanism put and make sure its a T104 with a 220v clock motor.
Got it. In either case, I am fine keeping the SWG at its standard 240V or do I need to change it to 120? Thanks again!No advantage to have pump powered direct from breaker vs line side of timer.
Do to NOT want more than one wire attached under the screw at the breaker itself. At the timer, you can put one wire to the left and one wire to the right of the screw threads.
Or you can pigtail three wires together using an appropriate wirenut - one from the breaker, one to the timer and one to the pump.
Nope - the SWG is being controlled thru the timer - that's why you need the ON/OFF clogs for the timer.
- That's a 20 amp breaker. Use 12awg solid conductor wire. Just run over to HD or Lowes and buy a couple feet. Looks like you may need to extend the pump wires as well, so get enough to do that and also a couple of wire nuts to accommodate two 12 gauge wires.
- Yes - you are connecting the wires from the breaker and the pump under the same screws on the timer.
- Yes.
With a T104 timer - lugs 1 and 3 are line - lugs 2 and 4 are load. Notice that the 2 white timer clock motor leads are wired to lugs 1 and 3 so they receive constant power to keep time.
Pop the timer mechanism put and make sure its a T104 with a 220v clock motor.
What is your intended use of the conduit/whip?This might be a dumb question but I’ve got the timer trippers in my basket and I noticed they sell pre-wired 10awg conduit. Since I’ll want the whip for the Circupool Control panel to pool subpanel. I was wondering if I could just use the 10 gauge that comes with the whip to power my timer from the breaker?
What is your intended use of the conduit/whip?
Not really. I don't think you can create a water-tight connection on the controller side.To protect the power cord coming from the SWG controller to pool electrical panel. Not needed?
Thank you
No, you cannot. A power cord strain relief that utilizes a half inch knock out is all you need.Not really. I don't think you can create a water-tight connection on the controller side.