What size breaker do I need?

Mleads310

Member
Aug 23, 2021
17
New York
Surface
Vinyl
Chlorine
Salt Water Generator
SWG Type
Hayward Aqua Rite (T-9)
Have a new pool install going and trying to get the parts list needed for Siemens panel. Have two pumps
Hawyard:
SP3215X20XE
And
HL32900VSP

What size breakers do I need for these pumps? Called Hayward, they stated to look on the pump and don't go more than 10 percent higher that amp draw??? Little concerned that they don't have the size breaker listed.

Also I know the VSP pump would need a double pole breaker, but the other pump I believe is single speed. Does this pump run on single or double phase?

Thanks in advance for any help.
 
You will need two ground-fault circuit breakers, one for each pump, according to the National Electrical Code. Since you will be running 240 volts on each pump you will need double-pole breakers. If there is nothing else on the same circuit (i.e. booster pump) you can use 15-amp breakers on each. If there is a booster pump on the circuit with the filtration pump you would need a 20-amp breaker.
 
  • Like
Reactions: Mleads310
 
  • Like
Reactions: Mleads310
Welcome to TFP.

What size wiring are you using between the CB and pump?
 
  • Like
Reactions: Mleads310
Thank you very much for all quick and helpful responses.
-booster pump. I don't believe there is one in the system but I will double check today. The pool builder installed the system (minus the electric). I do believe there is a turbo cell? Is that the same as a booster?
-definitely Siemens GFCI breakers that seems to be coming up a lot with these pumps.
-the wire gauge will depend on if I need a 15 or 20 amp breaker. I'm thinking 10 gauge for the 20 amp and 12 for the 15amp breaker.
 
-the wire gauge will depend on if I need a 15 or 20 amp breaker. I'm thinking 10 gauge for the 20 amp and 12 for the 15amp breaker.

Use 12 gauge for 20 amps circuits and 14 gauge for 15 amp circuits.

I would put in two 20 amp 12 hauge circuits even if you can get away with a 15 amp circuit. That way you can replace the pump with a 20 amp pump in the future without any problems.
 
The Pentair breakers are made by Siemens.

Siemens used to make a 20 amp breaker, but they discontinued it for some reason.


You can use a 30 amp breaker as long as the wire is big enough.

10 gauge from the breaker to the pump should be fine.

[edit]Based on the manual, I would use the Siemens 15 Amp Double Pole Type QPF2 GFCI Circuit Breaker.

[end edit]


I would recommend a 2.7 hp Tristar for the main pump.


What is the extra pump for?
 
Last edited:
I would put in two 20 amp 12 gauge circuits even if you can get away with a 15 amp circuit. That way you can replace the pump with a 20 amp pump in the future without any problems.
 
Are you providing the wire and doing the wiring or an electrician?
 

Enjoying this content?

Support TFP with a donation.

Give Support
wire-size-table-CU.png

1637001479859.png
 
The Pentair PA220GF is still available although pricey. I paid $130 in March and it is now $195.
That's why I would go with the 30 amp Siemens from Home Depot.

[edit]Based on the manual, I would use the Siemens 15 Amp Double Pole Type QPF2 GFCI Circuit Breaker.

[end edit]

1637001721790.png
 
Last edited:
If you are getting Hayward equipment, I would recommend the OmniLogic with subpanel.

Get the salt system included.

OmniLogic.jpg




 
If you are getting Hayward equipment, I would recommend the OmniLogic with subpanel.

Get the salt system included.

OmniLogic.jpg





Why the OmniLogic and not the newer OmniPl that you can also get with the TCELL940 SWG?

 
Why the OmniLogic and not the newer OmniPl that you can also get with the TCELL940 SWG?

If it's a better price, then it might be a better value.

In my opinion, they make too many versions of basically the same thing which causes nothing but confusion.

Just make a single system and be done with it.

You don't need 20 versions of the automation system.
 
If it's a better price, then it might be a better value.

In my opinion, they make too many versions of basically the same thing which causes nothing but confusion.

Just make a single system and be done with it.

You don't need 20 versions of the automation system.

My understanding is the OmniPl has an improved UI over the OmniLogic and is easier to use.

I agree Hayward has too many Omni automation versions.
 
Here is what the installation manual says to do.

Based on the manual, this is the one to get.

4.6. Electrical Specs

Refer to motor nameplate for voltage and current ratings. Use copper conductors only. For indoor & outdoor use.

Connect pump to a 15 amp branch circuit for 230VAC or a 20 amp branch circuit for 115VAC in accordance with local codes, regulations, and the National Electric Code (NEC).

A disconnecting means located at least 5 ft. from the inside wall of the pool, spa, or hot tub must be provided.




siemens-double-pole-breakers-us2-qf215ap-64_1000.jpg
 
Last edited:
Just to give a little background. The pool builder is installing a 20x14 pool, 80"x80" hot tub, run all plumbing to and from pool/hot tub and tie into pump in the pump room, run wires for lighting from pool to pump room.
I'm personally doing the feed from the main panel in house to sub panel in the pump room, which is completed.
I'm having an electrician, hasn't come to give estimate yet, do everything from the sub panel to the pump including the Omni 900, both pumps lighting etc.

I know absolutely nothing about wiring the Omni , relays , salt system etc. I do know it's going to be a salt water pool with Omni. Other than that I'm completely lost when it comes to pool equipment.

I'm trying to set up the electrician with all the breakers he needs in the sub panel prior to getting here for an estimate as I know these GFCI Siemens breakers have been hard to come by recently and figured I would get a jump on things for him.

I have attached a few pictures of my pump room set up and Omni equipment for reference. Again when it comes to pool stuff I'm lost, so bear with me.
 

Attachments

  • PXL_20211116_005735678.jpg
    PXL_20211116_005735678.jpg
    469.3 KB · Views: 13
  • PXL_20211116_005739173.jpg
    PXL_20211116_005739173.jpg
    462 KB · Views: 13
  • PXL_20211116_005746902.jpg
    PXL_20211116_005746902.jpg
    532.5 KB · Views: 12
  • PXL_20211116_005751986.jpg
    PXL_20211116_005751986.jpg
    471.9 KB · Views: 9
  • PXL_20211116_005756508.jpg
    PXL_20211116_005756508.jpg
    451.8 KB · Views: 10
  • PXL_20211116_005801007.jpg
    PXL_20211116_005801007.jpg
    374.7 KB · Views: 9
  • PXL_20211113_212518206.jpg
    PXL_20211113_212518206.jpg
    293.6 KB · Views: 9
  • PXL_20211113_212516722.jpg
    PXL_20211113_212516722.jpg
    234.8 KB · Views: 12
  • PXL_20211113_212503922.jpg
    PXL_20211113_212503922.jpg
    509.7 KB · Views: 45
  • PXL_20211109_220710349.jpg
    PXL_20211109_220710349.jpg
    540.4 KB · Views: 16
You will need two ground-fault circuit breakers, one for each pump, according to the National Electrical Code. Since you will be running 240 volts on each pump you will need double-pole breakers. If there is nothing else on the same circuit (i.e. booster pump) you can use 15-amp breakers on each. If there is a booster pump on the circuit with the filtration pump you would need a 20-amp breaker.
For any VS Pump/Filtration Pump, I would never run anything else on that breaker, no matter how small. A single speed pump you could but just do the math minus 20% max and you have your breaker amps. As noted, all breakers should be GFCI
 
  • Like
Reactions: Mleads310