Have you done any service work lately, and noticed a spark as you connect or reconnect the grounding electrode conductor to the ground rod of what appeared to be a perfectly normal electric service?
Have you ever disconnected the grounding electrode conductor at a water pipe and received a shock?
Have you ever noticed any arcing or sparking at a loose grounding electrode conductor at an outbuilding that has a connection to its own separate ground rod?
If you answered “yes” to any of these questions, the culprit is more than likely currents in the grounding electrode conductor.
The case of the open neutral.
In a properly functioning electrical system, the neutral conductor carries the imbalance current of the system.
For a single-phase system, the imbalance is the difference between the currents in the two “hot” legs of the transformer.
The current imbalance needs to return via the neutral conductor back to the transformer.
But, if that neutral is open, the imbalance current will seek other paths to get back to the neutral leg of the transformer.
At the main service, the neutral and ground are connected via the main bonding jumper.
If the ground path has a low enough resistance, it may prove to be a satisfactory return path, and the imbalance current will travel through the main bonding jumper into the grounding electrode.
Since the transformer neutral is grounded by the utility, and since the main bonding jumper connects the neutral and grounding conductor at the service, as per NEC requirements, the ground path provides a complete return for the imbalance current.
Even though the building you're working on may have a completely continuous neutral back to the transformer, the house next door or a building somewhere in the general vicinity may have an open neutral.
If the building you're working in and the building with an open neutral have some type of conductive path between them, current may return via that path.
A metal water pipe is a good example of such a connection.
Current can come “up” through a ground rod or a water pipe into the building you're working on, due to an open neutral in a neighboring building.
Is the current coming or going?
So now you're convinced that there can be current flowing in a grounding electrode conductor.
Next time you're on-the-job, use your ammeter to measure the current in the grounding electric conductor before you open up that connection.
If you measure a current, how do you know if it's due to current going “down” into the ground at this building or current coming up through the grounding electrode conductor in your building and returning back to the source via your neutral?
Unfortunately, putting an ammeter on the conductor will only prove that there is current flowing in the conductor.
It does not tell you the direction of that current.
You must use Kirchoff's Law to determine the direction of the current flow.
Kirchoff's Law states that all currents entering a connection are equal to the currents leaving a connection.
Simply put, all currents must balance.
Example No. 1. You're working on a single-phase, 120/240V service.
You measure 11A in the black conductor at the main service panel.
You measure 5A in the red conductor at the main service panel.
On a single-phase service, the neutral current is the difference between the two legs of the transformer, which in this case is 6A.
Therefore, if you measure 6A in the grounding electrode conductor and 0A in the neutral service entrance conductor, you can be relatively certain that the neutral is open, and your building is dumping current into an alternate return path (i.e. the grounding electrode).
Example No. 2. You're working on a single-phase, 120/240V service.
You measure 11A in the black conductor at the main service panel.
You measure 5A in the red conductor at the main service panel.
As in the first example, the neutral current will be the difference between the two legs of the transformer, which is 6A.
However, this time you measure 8A in the grounding electrode conductor.
How can this be?
Can there possibly be more current being dumped into the ground by the system you're working on than the system imbalance current?
Are there 2A of extra phantom current?
When you measure the current in the neutral, you find 14A.
Now you're really confused.
Applying Kirchoff's Law to the circuit, you quickly realize that the 6A of current imbalance from the system you're working on is being joined with 8A coming into this system from somewhere else.