Replace manual timer w wifi Suraielec

Shai

Member
Nov 23, 2023
13
NJ
Pool Size
35000
Surface
Plaster
Chlorine
Liquid Chlorine
Trying to wire the new suraielec wifi timer.
The provided diagram isn't easy to figure out.
I have a heater and a pump connected to the manual timer so when I move the little silver lever it turns both off or on.
My current right metal wire pipe is to the heater, the middle to the pump and the left goes to the circuit breaker.
I'm not sure if I have 110 or 220, the heater is gas, and my house is all 110.
Which wire/ s goes where on the new box?
The provided diagrams from the manufacturer are not in English :) I have no idea what they mean.
 

Attachments

  • 20240726_174800.jpg
    20240726_174800.jpg
    328.1 KB · Views: 8
  • 20240726_172401.jpg
    20240726_172401.jpg
    573.1 KB · Views: 7
  • 20240726_172410.jpg
    20240726_172410.jpg
    505.2 KB · Views: 8
  • 20240726_174423.jpg
    20240726_174423.jpg
    444.3 KB · Views: 7
  • 20240726_174451.jpg
    20240726_174451.jpg
    311.5 KB · Views: 7
  • 20240726_174752.jpg
    20240726_174752.jpg
    349.1 KB · Views: 6
  • 20240726_174754.jpg
    20240726_174754.jpg
    297.8 KB · Views: 5
  • 20240726_174758.jpg
    20240726_174758.jpg
    339.9 KB · Views: 5
  • 20240726_174535.jpg
    20240726_174535.jpg
    305.4 KB · Views: 8
  • 20240726_174520.jpg
    20240726_174520.jpg
    821.4 KB · Views: 16
FYI.

This wiring does not look to code. Romex should not be sued for outdoor wiring. Critters can chew on the wires. All outdoor wiring should be THWN wire in conduit.

20240726_174520-jpg.599809
 
  • Like
Reactions: Shai
Shai,

Your timer is set up for 240 volts AC..

Old timer to New timer

Move the wires on Pin 1 to Com 1

Move the wires on Pin 2 to NO 1

Move the wires on Pin 3 to Com 2

Move the wires on Pin 4 to NO 2

Add Jumper from Com 1 to L

Add Jumper from Com 2 to N


Thanks,

Jim R.
 
  • Like
Reactions: Shai
Shai,

Your timer is set up for 240 volts AC..

Old timer to New timer

Move the wires on Pin 1 to Com 1

Move the wires on Pin 2 to NO 1

Move the wires on Pin 3 to Com 2

Move the wires on Pin 4 to NO 2

Add Jumper from Com 1 to L

Add Jumper from Com 2 to N


Thanks,

Jim R.
Jim you are incredible. It worked. Given the old timer has no insulation with pin marking I google a bunch of images to I saw that they come w insulation with pin number designations, so I followed your map and it works!!
Can you please private message me your PayPal or Venmo? I'd like to send you a thank you gift.

Thank you everyone else for the help, yes the wiring was done by previous owner and I have no idea what their plan was, but it's a covered pump house so unless animals need 220v in their diet im good till we save for a pool system upgrade :)
 
Shai,

Thanks for the thought, but there is just no need to send me any gifts... I volunteer to do this, just to help people like you...

That said.. I would not have a place to volunteer, if it were not for TFP.. I suggest that you become a supporter, to help keep the TFP doors open...


Glad everything worked out ok for you...