Raypak heat pump

mikerad

New member
Apr 25, 2024
2
New york
I just bought a Raypak 138k heat pump. The manual (see picture) says I need a 60-amp breaker and can run #8 THHN if I am within 110 feet of the pool. I'm only 25-30 feet away. Does that wire size sound right or should I increase it to #6 THHN?
 

Attachments

  • Screenshot 2025-03-21 102226.png
    Screenshot 2025-03-21 102226.png
    18.2 KB · Views: 8
Welcome to TFP.

Never hurts to use the larger wire size except in your wallet.
 
#8 AWG THHN is ok for this installation as specified by the manufacturer.

Ampacity and rating.

The manufacturers of hermetic systems supply the correct protection, conductor sizing, and other information on the equipment nameplate.

Use this information when wiring an air conditioner or other hermetic motor equipment.

1742568025906.png

1742568063050.png

1742568677544.png
NOTE: Refer to the National Electrical Code, Article 680, for general requirements for swimming pools and equipment, and to Article 440 for special considerations necessary for circuits supplying hermetic refrigeration motor/compressors.




1742568934303.png

1742569059109.png
 
Last edited:
TFP is a registered 501(c)3 non-profit that is maintained by user donations.

The people who answer questions are volunteers.

If you find the site to be a good resource, please consider making a donation to help support the site.

Thanks.

 
That's a great link, I think, provided by @JamesW - What Most Techs Get Wrong About Wire Sizing, explaining how and why the NEC/NFPA allows manufacturers to set the smaller #8 as acceptable in this case. I still might consider upsizing to #6 to allow for a future equipment change - perhaps for a bigger heater or one with different specs.