A very weird problem with the Raypak 007864F igniter in my Raypak 406A spa heater has arisen; I'm wondering if anybody else has seen it. The control board always reports "Flame w/o CFH" even with the bare igniter entirely removed from the heater & pilot assembly and grounded only at the small metal bracket mounted on the insulator. If the wire to the igniter is unplugged at the board, the board does not report any error. This phenomenon is 100% reproducible.
Both the +- 1V/uA on-board readout and a direct measurement in series to the igniter indicates ~0.8 uA DC current with about ~22 VAC being applied. It is clear that something is acting as a diode within the insulator - probing over the surface of the insulator with the ground lead does not result in any current. Ideally, with the igniter removed & cold there should always only be 0 uA. Bypassing the blue HV wire by connecting to the flame end wire gives the same DC current.. It is quite clear that the rectification cannot be any artifact of the PC board.
While replacing the igniter is the obvious next move, has anyone else ever seen rectification through a 007864F insulator?
Both the +- 1V/uA on-board readout and a direct measurement in series to the igniter indicates ~0.8 uA DC current with about ~22 VAC being applied. It is clear that something is acting as a diode within the insulator - probing over the surface of the insulator with the ground lead does not result in any current. Ideally, with the igniter removed & cold there should always only be 0 uA. Bypassing the blue HV wire by connecting to the flame end wire gives the same DC current.. It is quite clear that the rectification cannot be any artifact of the PC board.
While replacing the igniter is the obvious next move, has anyone else ever seen rectification through a 007864F insulator?