Code will not allow for thhn out of conduit or a cable tray. I know where you are coming from thinking it doesn't need it but code requirers it.
Also with a run of 270 feet to get a 60 amp run with a voltage drop of less than 3% you are looking at #2 wire. The best you can get with #6 wire is 40 amps which is a marginal at best 4.4% voltage drop for a 270 foot one way run. As it is you should have had #8 wire for 110v/20amps at a run that long. 12 gauge gives a voltage drop of almost 18% for a 270 foot run at 110v/20amps.
They were all on 20 amp breakers, but none of them were drawing anywhere near that. The biggest load was the main pump at I think 8.4 amps on high. The 200ft run would keep it at a lower voltage drop. I'll see how much #4 and #2 are tomorrow. If it's not too much more, I may up the size; otherwise I guess I'll just de-rate it to 40 amps. It would be nice to have the available power to put in a heat pump if I wanted one day.