Cycled power at the breaker today and received first low voltage error
Cycled power at the breaker today and received first low voltage error
So electricians came out and changed a wire and it ran for two days and then started doing it again. I went ahead and wired in a hard start capacitor and it started right up. Will watch it.What breaker feeds this subpanel?
How far is it from the main panel to this subpanel?
What is the wire size from the main panel to this subpanel?
What is the wire type?
Did you watch the voltage before anything turns on and then when heat pump turns on?
You need to measure the voltage with no load, during startup and during operation.Is there a chance my voltage varies out here and that’s why it’s hit or miss?
Are the electricians not checking the voltage and giving you a report?Is there a chance my voltage varies out here and that’s why it’s hit or miss?
They are a licensed firm and reputable. They said they had good voltage to the unit the entire time but again, it happened to start after they ran a new wire that day. It’s been hit or miss the entire time I’ve had it. Sometimes power flickers in the house when I try and turn it on and sometimes it kicks on and no issue at all. So far the hard start kit has worked and it’s kicked it on a couple times since I’ve installed it. I am going to have a different electrician look at it and get a second set of eyes, primarily looking at wire size.Are the electricians not checking the voltage and giving you a report?
What exactly are they doing?
Seems like they should be able to tell you what's up.
Are they licensed master electricians or just unskilled helpers being sent out to try random things with no real idea what they are doing?
Not sure if they are master electricians but I am going to find a different one. Service anymore is a joke.Are the electricians not checking the voltage and giving you a report?
What exactly are they doing?
Seems like they should be able to tell you what's up.
Are they licensed master electricians or just unskilled helpers being sent out to try random things with no real idea what they are doing?
That indicates a bigger issue.Sometimes power flickers in the house when I try and turn it on and sometimes it kicks on and no issue at all.
Ok. In the meantime, could I be doing damage using the hard start kit?Your pump is indicating low voltage and the flickering is also indicating voltage problems.
Definitely need to get a licensed master electrician to check it out.
There might also be a problem with the compressor and you can have that checked by an HVAC tech, but I would make sure that the voltage is staying good first.
The wiring color scheme inside the box is odd. A wire that is wrapped with white tape is inserted into the load side of the breaker. White is reserved for neutral. If you wanted to distinguish between the 2 wires going into the 50 amp breaker on the left, balck and red would be the most common color choices. You should remove any white tape on both ends. If you want to keep track of which wire is which - not necessary on 220V circuits, but not prohibited, you should wrap both ends with red or a color other than white, green or gray. This is not the source of your issue but it is a safety issue. White and gray wire colors are reserved for grounded coonductors (aka neutral) and are expected to be tied into the neutral bus bar (at the top) and green colored wires are reserved for equipment grounding conductors (aka grounds) and are expected to be is tied into the ground bus bar (on the left).
Which hard start kit did you use?Ok. In the meantime, could I be doing damage using the hard start kit?
SUPCO SPP6. Sized for up to 120k BTU / 230/1. The problem has gone away and I can tell it’s a lot smoother start when the compressor kicks in. Wired to Herm and compressor on capacitor, that’s all that was requiredWhich hard start kit did you use?
How was it wired in?
Does it start better, worse or about the same?