Bugs are when a feature is not functioning as specified.
Implementing a temperature delta for freeze protection is a new feature request.
Pentair designers were simpleminded when they specified how Freeze Protection should work.
Pentair designers do not appear to own and maintain pools and use their own products. If they did the short comings should be obvious to them as it is to their customers.
Uhh....... in what world does freeze protection cycling on and off every 10 seconds constitute requesting a new feature? The old easytouch ran pumps for quite a period of time until the system was sure the freeze event was over. Turning a pump on and off every 10 seconds causes equipment damage. It should not be a feature request to not damage equipment. Pumps, seals, motors, the windings of the motors, the relays to start, are all over stressed in this scenario.
To be clear, no one is asking for some odd temperature delta. If freeze protection activates, make the Dang thing run for 20m or so and check the temperature again. Its not rocket science.
For reference, i took this video on 2.xx firmware but it does the same thing on 3.002. Note how 35F turns on protection, and 36F turns it off. This shows that the protection is tied directly to a temperature sensor without any dead band built in. Proper control would be something like ON=35F, OFF=37F. Again, not rocket science.