- Sep 15, 2020
- 14
- Pool Size
- 15000
- Surface
- Plaster
- Chlorine
- Salt Water Generator
- SWG Type
- Pentair Intellichlor IC-40
Pentair Intellicenter panel (521906). Ultratemp Heat Pump set in Remote Mode "Relay". Always has been this way. Heat pump was running fine, then stopped even though the Intellicenter display shows it is heating. Noticed the temp sensor wire was broken, fixed it and it shows temp on display but still will not start heat pump at set point. To check existing wire, ran temp wire from heat pump control board to intellicenter control board but heat pump still doesn't work. Replaced the control panel on heat pump. Heat pump still won't run. On the heat pump menu, switched Remote Mode from "Relay" to "Off" and the heat pump immediately started heating. Switching back to "Relay" shuts off the heat pump. Is this a intellicenter circuit board problem or should I test/replace one of the relays? How should I test the relay to see if it is the problem? How can I test the circuit board to see if it is the problem?
Thanks in advance
Thanks in advance