Hello all,
I'll try to make this brief as it's been a strange six week ordeal with my heater, but after 4 tech visits and a lot of "opinions", I am beginning the question the help I'm getting. I may say a few things incorrectly as I am still learning how heaters work and the proper terms.
Pool specs: 10,000 gallon AGP, Backyard Systems/Waterway II filter/pump system (2-speed), less than 4 feet of water piping between every component.
Issue: Six month old Mastertemp 125 hits hit temp (SFS) limit (480 degrees) and shuts down within 10 minutes. No error codes - just service heater light.
History: Ran fine last season but we only had about six weeks of operation as the pool wasn't done until August (I live in Ohio). Fired it up mid-April and started to see the issues. I called my pool installer first and a heater guy came out, opened up the manifold and saw calcium deposits. He "chemically cleaned" the heater, closed it up and called it a day. Issue recurred. Same guy came back, cleaned it again (more deposits/pieces had broken loose and were sitting in the manifold). Issue recurred. I called Pentair, who had a warrantied support guy come out. This guy checked to make sure the SFS was working and he said it was fine. He checked the gas flow, said water column was within spec. He took the unit apart, saw sooting in the heat exchanger and some of the fins were clogged up (I saw this, forgot to get a picture).. Anyhow - after all that, the main issue still recurred. I'm waiting on my second warranty visit now.
Some more info: No corrosion issues seen when unit was disassembled. First tech said my water balance was way off (high alkaline) and that caused the deposits. I pulled my test history (I went weekly to have it checked by someone other than me) and this is not the case. pH was 7.8 for about 2-3 days and I corrected it (was 7.4 next reading, within 3 days of the 7.8). Either way, there was never a sustained out of balance time period during the six weeks the pool was in use. Second tech guy said wind could be causing a 'reburn' of exhaust (high winds not allowing the flue to disperse properly. Yes, we live near Lake Erie and do get high winds. The unit is not enclosed in any way, but unless the wind was high every single day (it wasn't), I can't see this happening when the heather ran for 2-3 hours per day in the morning to regain lost temp overnight.
So, it appears there may be two issues, but I can't say that either of them are directly related to the overheating, especially since "both" have been "resolved" and the overheating still occurs. Water flow rate at the high pump speed is very strong. At the low pump speed, it's not and seems weaker than it was last year, however I know you should use the higher speed. Last season, I did NOT do this (I wasn't told anything about this but my flow rate should be 20-100 at any given time). I have replaced the filter, run the system without filter (and without the Frog chlorine pack just to ensure exit flow isn't being restricted). I know this unit has a lot of built-in systems to prevent damage (internal bypass, flame/burn sensors) so I am just baffled how things got bad so quickly.
That's a huge post - I'm just not sure where to go from here. Everyone's busy now since it's pool season in Ohio, which is one reason I opened my pool so early (April) but that hasn't proven to be worth it without a working heater. I'm so frustrated. How can I wreck my heater (if I did) in six weeks. I'll take responsibility for that, but I want to stop this from recurring.
Thanks for any feedback.
I'll try to make this brief as it's been a strange six week ordeal with my heater, but after 4 tech visits and a lot of "opinions", I am beginning the question the help I'm getting. I may say a few things incorrectly as I am still learning how heaters work and the proper terms.
Pool specs: 10,000 gallon AGP, Backyard Systems/Waterway II filter/pump system (2-speed), less than 4 feet of water piping between every component.
Issue: Six month old Mastertemp 125 hits hit temp (SFS) limit (480 degrees) and shuts down within 10 minutes. No error codes - just service heater light.
History: Ran fine last season but we only had about six weeks of operation as the pool wasn't done until August (I live in Ohio). Fired it up mid-April and started to see the issues. I called my pool installer first and a heater guy came out, opened up the manifold and saw calcium deposits. He "chemically cleaned" the heater, closed it up and called it a day. Issue recurred. Same guy came back, cleaned it again (more deposits/pieces had broken loose and were sitting in the manifold). Issue recurred. I called Pentair, who had a warrantied support guy come out. This guy checked to make sure the SFS was working and he said it was fine. He checked the gas flow, said water column was within spec. He took the unit apart, saw sooting in the heat exchanger and some of the fins were clogged up (I saw this, forgot to get a picture).. Anyhow - after all that, the main issue still recurred. I'm waiting on my second warranty visit now.
Some more info: No corrosion issues seen when unit was disassembled. First tech said my water balance was way off (high alkaline) and that caused the deposits. I pulled my test history (I went weekly to have it checked by someone other than me) and this is not the case. pH was 7.8 for about 2-3 days and I corrected it (was 7.4 next reading, within 3 days of the 7.8). Either way, there was never a sustained out of balance time period during the six weeks the pool was in use. Second tech guy said wind could be causing a 'reburn' of exhaust (high winds not allowing the flue to disperse properly. Yes, we live near Lake Erie and do get high winds. The unit is not enclosed in any way, but unless the wind was high every single day (it wasn't), I can't see this happening when the heather ran for 2-3 hours per day in the morning to regain lost temp overnight.
So, it appears there may be two issues, but I can't say that either of them are directly related to the overheating, especially since "both" have been "resolved" and the overheating still occurs. Water flow rate at the high pump speed is very strong. At the low pump speed, it's not and seems weaker than it was last year, however I know you should use the higher speed. Last season, I did NOT do this (I wasn't told anything about this but my flow rate should be 20-100 at any given time). I have replaced the filter, run the system without filter (and without the Frog chlorine pack just to ensure exit flow isn't being restricted). I know this unit has a lot of built-in systems to prevent damage (internal bypass, flame/burn sensors) so I am just baffled how things got bad so quickly.
That's a huge post - I'm just not sure where to go from here. Everyone's busy now since it's pool season in Ohio, which is one reason I opened my pool so early (April) but that hasn't proven to be worth it without a working heater. I'm so frustrated. How can I wreck my heater (if I did) in six weeks. I'll take responsibility for that, but I want to stop this from recurring.
Thanks for any feedback.