From the pool panel, I see three feeder wires coming in, white, blue and dark green. Is the dark green ground or neutral?
Refer back to this pic.
Blue and white wires are connected to hot bus.
Green wire connected to ground bar.
From the 30A breakers at main panel, I see two wires one red one white.
You need to do some further digging if the red wire becomes a blue wire and find an intermediate junction box.
Follow that conduit out of the lower right of the outdoor panel to the junction box below it.
The only option for GFCI to work is to fish a separate natural wire from the pool panel back to the main panel and plug into the netural bus?
Yes.
Or put a small subpanel next to the main panel that will fit a GFCI CB.