Re: Wiring Intelliflo Pump to Easy Touch panel
OK - I completed my re-wire yesterday based on everything I read on this site and in the Pentair Manual.
Previously my VS Intellipro pump had been wired to the Pump Relay -- I have removed the connection to the relay and wired the pump directly to the 20A Dual Pole 240V GFCI Breaker. This breaker now only powers the pump and is not connected to anything else (I believe this was the source of my initial problems as this breaker was also powering my Intellichlor IC40 Tranformer via the relay.)
I have another 20A Dual Pole 240V GFCI Breaker in my box which is wired to Relay #2 -- this was previously powering my Blower and the EasyTouch Transformer (my EasyTouch is wired for 240V). I simply added jumper wires from the Relay #2 LINE screws to the Relay #1 (PUMP) LINE screws. I did not change any wiring for the Intellichlor IC40 as this was already wired to the LOAD screws in Relay #1.
In summary, my first 20A Dual Pole 240V Breaker is now wired directly to my VS pump and is not connected to any relay. My second 20A Dual Pole 240V Breaker is now wired to Relays #1 & #2 via jumper wires - this is powering my Intellichlor Transformer on Relay #1 and my Blower on Relay #2. My Easytouch Transformer is also connected to the LINE screws in Relay #2 to pull power off this breaker.
Does anybody foresee any issues having the Blower, EasyTouch Transformer, and Intellichlor Transformer all wired to the same 240V 20A GFCI breaker --- the only addition to this breaker from my prior setup is the Intellichlor transformer.