Brand New Hayward H500 not workin

Jun 4, 2009
106
Sullivan County, NY
I bought a replacement for a broken H500 in the Fall and just installed it today.

The system fails with an A0

I've read that A0 means the vacuum sensor is not reading a vacuum -- either the fan motor is not creating the vacuum or the sensor is no good.

The fan is spinning nicely, and the unit is brand new. Totally clean inside, vacuum and pressure hoses nicely pushed on to both the fan housing and the sensors.

It's been too long to go back to the vendor.

I was hoping that because the propane gas pipe sat turned off all Winter, maybe it just needed time, but it's been a couple of hours of trying to make this work.

What should I do?

Thank you!
 
What is the supply voltage?

It looks like the old one was connected to 120 volts.

If the input voltage is 120 and the heater is set to 240 volts, the fan will run too slow.

Note: Do NOT put 240 volts on a heater set to 120 volts or the heater will be damaged.

1652394931892.png


1652394727633.png
 
Last edited:
Wow!

The heater was being fed 120v (1 hot, 1 neutral).

When I changed the plug on the motherboard, I could hear the fan spinning much faster.

So that fixed the A0 error.

But now, immediately upon power up, CE flashes and then changes to 5F (could be SF).

Googled it and found it 5F indicates a faulty temperature sensor.

But, seeing as I've messed this up from the get-go, perhaps I'm missing something else?

Is the conversion from 240 to 120 more than the single jumper-plug on the control board?

Any other ideas?

Thank you!
 
The conversion should be just the plug.

The sensor wiring might be loose.

Check all wiring.

Is the water flow good?

Do you have an external bypass?

View attachment 409868
View attachment 409871
View attachment 409872

Wiring from thermistor to connector on control board appears fine.

Water flow is at 90gpm.

I do not have an external bypass.

I've ordered a new sensor. Seems Hayward changed the sensors they use from FDXLTER1930 to FDXLTER1931 (so it will take a few extra days to get to me; and to know if the problem really is a bad sensor).

Anything else I can do or check?
 
I just tested the resistance at the control board side of the wire coming from the sensor and both black-red1 and black-red2 are both just under 13kohms.

From what I can find online, that corresponds to about 66*f, which is the water temp.

Yet I still have an SF error.

I will take a video, but in the meantime, upon power up I get CE for about 1 second then it changes to SF.

Is there such a thing as a factor reset for the control board?
 
If I understand correctly, the resistance tests shows that the sensor is good. That means it could be the control board. Is there anything else it could be?

Here are a couple of videos.



Ignore the flickering -- it doesn't flicker in real life, must be refresh rate thing
 