I plumbed in a new aquacal sq225 a little over a month ago. I placed the flowvis meter after the heater since it acts as a check valve/bypass. With fresh DE and the pump running at max 3400 rpm, the meter reads about 38gpm. Heater min/max flow is 30/70. My pump typically runs at 2100rpm which shows about 28-30gpm on the meter which activates the heater.
Aqucal tech said the optimal flow for this heater was 40-45gpm. He said I should have placed the flow meter before the heater inlet to get an accurate gpm. I explained the flow meter doubled as a check valve and acting as a bypass which he understood. However, he still stated in order to get the correct flow entering the heater I should add another flow meter at the heater inlet. Is this correct?
He also went on the check the water inlet and outlet temps at the skimmer and return jet.
2100 rpm - 9°
2400 rpm - 8°
2700 rpm - 7°
3000 rpm - 6°
The directions for this model regarding delta-t state 4-9° difference is optimal.
Where is the happy medium here? Should I be more concerned with achieving the optimal gpm of 40-45 gpm? Or, finding the correct rpm that puts the delta-t somewhere in the middle of 4-9°?
Aqucal tech said the optimal flow for this heater was 40-45gpm. He said I should have placed the flow meter before the heater inlet to get an accurate gpm. I explained the flow meter doubled as a check valve and acting as a bypass which he understood. However, he still stated in order to get the correct flow entering the heater I should add another flow meter at the heater inlet. Is this correct?
He also went on the check the water inlet and outlet temps at the skimmer and return jet.
2100 rpm - 9°
2400 rpm - 8°
2700 rpm - 7°
3000 rpm - 6°
The directions for this model regarding delta-t state 4-9° difference is optimal.
Where is the happy medium here? Should I be more concerned with achieving the optimal gpm of 40-45 gpm? Or, finding the correct rpm that puts the delta-t somewhere in the middle of 4-9°?