When I opened my EasyTouch panel to wire my new blower to a relay, I noticed a couple of relays had a wiring I could not make sense of. Here are the pictures:


I don't understand the purpose of this wiring: it seems #4 and #6 are being used to connect wires together irrespective of the relay state. Am I understanding this right? Can I free these relays by replacing this with 4 pigtails/Wago connectors?
I'd also like to make sure I understand how these relays work. Let's say I pick AUX 6. There's _one_ relay for AUX 6, which has 2 control wires at the top that determine whether the relay is closed or open: these are connected to the board in the low voltage section.
If closed, 2 and 4 are connected, and 6 and 8 are connected. If open, they are not connected.
The left (2 & 4) and right (6 & 8) sides are independent, meaning that you can't connect 6 to your breaker and 4 to your load, and expect that current will flow from 6 to 4 when the relay closes.
Is that the behavior I should expect?
So now for my blower, I was going to pick one free relay, wire power from a breaker to #2, and the hot wire from the blower to #4. Then neutral & grounds with their respective bars. Does that sound correct? (it's a 120V blower, not 240V)
Thank you again!


I don't understand the purpose of this wiring: it seems #4 and #6 are being used to connect wires together irrespective of the relay state. Am I understanding this right? Can I free these relays by replacing this with 4 pigtails/Wago connectors?
I'd also like to make sure I understand how these relays work. Let's say I pick AUX 6. There's _one_ relay for AUX 6, which has 2 control wires at the top that determine whether the relay is closed or open: these are connected to the board in the low voltage section.
If closed, 2 and 4 are connected, and 6 and 8 are connected. If open, they are not connected.
The left (2 & 4) and right (6 & 8) sides are independent, meaning that you can't connect 6 to your breaker and 4 to your load, and expect that current will flow from 6 to 4 when the relay closes.
Is that the behavior I should expect?
So now for my blower, I was going to pick one free relay, wire power from a breaker to #2, and the hot wire from the blower to #4. Then neutral & grounds with their respective bars. Does that sound correct? (it's a 120V blower, not 240V)
Thank you again!