Twist lock spliter

DrinkBeer

Active member
Mar 3, 2022
26
NJ
So I know someone will say this is a no no.. but when i had my electrician run the electrical for my pump I didn't have plans for any other accessories. so i have a single twist lock at the pump. I want to setup a low draw led light and the only standard outlet is accross a stretch of grass.. :( its the utility outlet or maintenance outlet. My question is can i use a splitter at the twist lock by my pump that has a Standard outlet and twist lock and use it for led lights?

I'm thinking its a really bad idea.. since i cant find the splitter anywhere and may have to make one up myself.. (that i really rather not do)
 
So I know someone will say this is a no no.. but when i had my electrician run the electrical for my pump I didn't have plans for any other accessories. so i have a single twist lock at the pump. I want to setup a low draw led light and the only standard outlet is accross a stretch of grass.. :( its the utility outlet or maintenance outlet. My question is can i use a splitter at the twist lock by my pump that has a Standard outlet and twist lock and use it for led lights?

I'm thinking its a really bad idea.. since i cant find the splitter anywhere and may have to make one up myself.. (that i really rather not do)
Doesn't take much of an unbalanced load to trip a GFCI. Use one leg of that 240V receptacle for another purpose and, if noting else, you well may have nuisance tripping. If the light goes on with out the pump it definitely will trip.
 
  • Like
Reactions: Newdude
Thread Status
Hello , This thread has been inactive for over 60 days. New postings here are unlikely to be seen or responded to by other members. For better visibility, consider Starting A New Thread.