Spa light junction eliminate
kcindc
1,295
Fairfax, VA
My spa light has a junction box the sits in the middle of the yard. It is an eye sore and a tripping hazard. I need to replace the spa light as it doesn't work (rusted water inside probably circa 1980s). Is there a way to eliminate this and marry up the two conduits below ground without having to replace the entire conduit?IMG_0533.JPG thanks!
Short answer: no. I know I've seen pictures of flush-mounted boxes, so I googled and followed a link from an image to NEC Requirements for Installing Pools and Spas, Part 2 of 3
For luminaires greater than 15V, the junction box must be at least [680.24(A)(2)]:
4 in. above the ground or pool deck or not less than 8 in. above the maximum water level ( Fig. 2 ).
4 ft from the inside wall of the pool, unless separated by a solid fence, wall, or other permanent barrier.
For luminaires less than 15V, you can use a flush deck box if [680.24(A)(2)]:
An approved potting compound prevents the entrance of moisture.
The flush deck box is at least 4 ft from the inside wall of the pool.
If your pool lighting is low voltage, then you could dig things up and install a flush mount.
What I want to do is to join the two conduits eliminate the junction and put in a light with a cord long enough to reach from the spa to electrical breaker panel at my equipment pad.
Or if a junction is needed put it closer to the electrical panel instead of out in the yard without having to dig a whole new complete trench from the spa to the electric panel.
You need a junction box on 120v lights but you can move it near your panel. Keep in mind that you must also run a new #8 ground wire in the conduit (if the conduit is a non-metallic material).
The trouble you are going to have is splicing the existing conduit sections together and making them watertight if they are made of anything other than PVC.