SPA heater, what would happen?

You can check the gas pressure at the manifold.
I checked the gas pressure as suggested. The pressure were +3.62" and +0.04" as show the pictures below.

No gasWith gas (heating)
1736274058069.png1736274098647.png

12. Remove the barbed adapter. Apply joint compound to the NPT plug and replace to seal the vent port.

1735925474741.png
After adjusting the offset pressure screw, the value get around -0.2" (varied from -0.19 to -0.24)

1736274449154.png
 
  • Like
Reactions: JamesW
Ok, let's see if the numbers for gas used, temperature rise overall, temp rise for flow and stack temp are all where they are supposed to be.
Below the results of the temperature (according with heater display) in the time. Notes: it was a little rain

I will perform another test including the recording of the meter as well.

1736279601285.png
 

Enjoying this content?

Support TFP with a donation.

Give Support
The pressure test is somewhat confusing because both lines are under vacuum and you are taking a negative differential pressure, so it's like a double negative.

The Pressure tap side is lower pressure (more vacuum) before the gas valve opens because the gas line is closer to the blower impeller.

Once the gas valve opens, the gas pressure pushes the Pressure tap side pressure higher than the vent line side, which makes it read negative since the low side is now a higher pressure than the high side even though both sides are vacuum.

In my opinion, it would be clearer if they reversed the instructions to make the vent the low side and the pressure tap to be the high side and the reading should be +0.2" w.c.

As it is now, increasing the gas pressure makes the reading go more negative.
 
Last edited:
  • Like
Reactions: Hulaomr
Ok, let's see if the numbers for gas used, temperature rise overall, temp rise for flow and stack temp are all where they are supposed to be.

I did another test including:
  • Temperature (F) at the heater
1736284765633.png
  • Gas consumption at the meter
1736284806167.png
  • Stack flue temperature
    • In around ~3min it get to 333F.
Notes: this time it was sunlight and no raining
 
The gas used is about 3.4 cubic meters per hour, which is about 75% of the expected consumption of about 4.5 cubic meters.

You are getting about 0.79 degrees per minute, which is about 68% of the expected temperature rise of 1.16 degrees per minute.

It seems to be working, but not at 100% performance.

Hard to tell exactly why is is not at 100%.

Note that the tests are just estimates and they are not going to be 100% accurate.

Are you sure about the spa volume at 580 gallons?

Note that you will also lose some heat if the spa is uncovered, so that can affect the heating times and it can account for the total heating time being longer than expected.

Try to get a temperature before and after the heater with thermistors to see the temperature rise at 60 GPM.
 
Last edited:
  • Like
Reactions: Hulaomr
Here is what the normal exhaust temperature should be:
  • Below 250 degrees...very low
  • 250 to 290 ..................low
  • 290 to 350.................acceptable
  • 350 to 480 ..................high
  • Above 480...................error/shutdown.

Stack flue temperature
  • In around ~3min it get to 333F.
The Stack temperature is in the acceptable zone, which is good.

It might be working correctly and the gas consumption might not be 100% accurate.

With the correct manifold pressure, the gas supply should be ok.

Maybe an issue with air intake supply.

Inadequate air supply can cause incomplete combustion due to lack of oxygen and the reaction producing some carbon (soot) and some carbon monoxide instead of carbon dioxide.

Make sure that you have adequate air supply and adequate venting.

Improper venting is a serious safety hazard, so get this 100% correct with a qualified gas contractor before operating the heater.

The heating time can possibly be explained by heat loss.
 
  • Like
Reactions: Hulaomr
Are you sure about the spa volume at 580 gallons?
Ok. I calculate assuming two rectangles and the volume get to 2239.71 Liters. Similar to the one reported previously.

The 580 gallons come from drawing the SPA in a CAD software and calculate the volume based on a solid. It must be quite accurate (without the pipes).

1736288080418.png

1736287288909.png
 
  • Like
Reactions: JamesW
Note that you will also lose some heat if the spa is uncovered, so that can affect the heating times and it can account for the total heating time being longer than expected.
The SPA is uncovered all the time. Just has a metal (tubes) pergola.
 
  • Like
Reactions: JamesW
HEAT LOSS FROM WATER SURFACE AT VARIOUS AIR AND WATER TEMPERATURES AND AIR VELOCITIES AT 70% HUMIDITY.

1736288598775.png

 