[Solved] Rheem 406A Propane Heater not responding to remote signal

pacohope

Silver Supporter
Jul 5, 2023
4
Centreville, Virginia, USA
Pool Size
15000
Hi all, my first post here since actually registering. Really grateful to the community here.

I have a Rheem 406A Propane heater for a 15K gallon inground pool. Everything works totally fine in manual mode. I'm building my own pool controller based on a Raspberry Pi computer, an 8-switch relay, and some cool free software. Here's an example of the kinds of instructions I'm following.

I recently replaced the control board (a raypack 013464). The instructions say that you provide 24VAC on the blue wire, and then a path to common on either the black or the orange and that's how it knows whether you want spa temp, pool temp, or no heat. I've built this with my relays and it delivers what I think is the right electric signal in the right circumstances.

The problem is this: I put the heater into 'remote' mode (hold down temp up/down buttons for a few seconds). I trigger the voltage from my automation system. Nothing happens. I'll see 'remote. no demand' on the display. It never changes. If I take it out of remote mode, and I use the 'mode' button to turn it on/off and set temperatures, it works fine. E.g., putting into spa mode will spark and heat to spa temperature.

I took my electric meter out to measure the voltage at the heater. When I have it on, I see 28.8V AC on the blue/orange path (for example). Then I switch it and I see 28.8 VAC on the blue/black path. Then I turn it off and I see like maybe 1V AC. Interestingly, when I have 28.8 VAC running across one circuit, I seem to have about 10 VDC running on the other. At least that's what I *think* the readings show. (The "AC" on my multimeter disappears, and about 10.1 V appears on the display). That's weird. I don't know if it's an incorrect reading, related to my problem, or just spurious information.

Below is a wiring diagram of how it looks. If relay 7 is active, 24VAC flows from COM to NO ("NO" means normally open). Power then passes via relay 8. Either it goes over the NC (normally closed) path, which is the orange wire for pool temperature, or it flows over the NO path to the black wire, indicating spa temperature. If Relay 7 is off, no power flows at all. This seems like the right wiring. But the heater doesn't respond.

Anybody have ideas what I should try next?

Heater Remote.png
 
You should not be providing 24V from outside the heater. The heater provides the 24V and the automation just needs to complete the circuit with a relay between the COM and POOL or SPA line.
 
Which lines on the Rheem control board are POOL, SPA, & COMMON?
 
That was it! Thank you! The diagram I have above is what I used. It's working! The schematic is below. So you can see pin 1 is Black/Orange (I just use black) for pool. Pin 2 is orange/black (I use Orange) for spa. And pin 3 is blue for 24V.

Now, when I close relay 7, power flows from blue (in on common on the relay) out the NO terminal on the relay over to common on Relay 8. Then it flows back to the heater control over either black or orange, depending on the state of relay 8. For no heat, I turn off relay 7 (so no power flows) and I don't really care about the state of relay 8. For the to activate the two modes, I turn on relay 7, and then control relay 8 to get pool or to get spa.

Getting the right answer in less than an hour is freaking amazing. Thank you so much! I will now make a donation to the site. Worth every penny!
 