The manual has the following troubleshooting section, time to break out a multimeter. Also check the cable isn't damaged. If the circuit board is faulty, I'd recommend replacing with a Pentair SolarTouch (even a used on from eBay would work).
Water Flow To Panels Switch Does Not Operate The Valve Actuator
If the Valve Actuator does not operate when using the WATER FLOW TO PANELS Switch (sliding switch between ON and OFF), either the Valve Actuator or the Circuit Board is at fault.
First verify that the toggle switch located on the Valve Actuator is either in the ON1 or ON2 position.
With a voltmeter, check the output voltage of the VLV1 socket located on the LX-220 Circuit Board. When the WATER FLOW TO PANELS Switch is in the OFF position, the top and middle pins should read 24 VAC.
When the WATER FLOW TO PANELS switch is in the ON position, the top and bottom pins should read 24 VAC. If voltage readings are correct, replace the Valve Actuator. If voltage readings are incorrect, replace the Circuit Board.