@JamesW I received the oscilloscope, so I'll hopefully have time tonight to test it. I've had to redirect my focus multiple times; I wish I could clone myself to assist with all of the things to take care ofWhat is the conduit running from the meter socket to the main panel? If it's plastic, turn off the main breaker and lift the neutral coming from the meter socket. 180Hz like James said is the third harmonic and everything electronic can add to it. By lifting the neutral coming from the meter socket you are completely eliminating anything coming into you home from the power company. The reason it only works with plastic piping is the neutral is tied to the can in the meter.
Do you have any power backups on computers, TVs or anything else?
Being on the third harmonic it becomes a relationship between the neutral and the EGC which you have been playing with at the pump and timer. Might revisit the solar panels again, you turn off the breaker but did you lift or disconnect the neutral from the solar panel system? Photovoltaic inverters converting dc to ac are known sources of harmonics.
First off is making sure the pool area is safe by repairing the equipotential plane making sure it is in good order.
In other words don't be like thisI think that if you can watch the voltage, current, frequency and waveform while connecting or disconnecting different things, you should be able to see a change in all of the readings that corresponds to what you're doing when you get to the source of the stray current.
Note: Only do what you are 100% sure that you can do safely.
Consult a local professional expert for advice on anything that you are not 100% sure about.
If you do this make sure they lift the neutral in the meter as well. This will eliminate any transients coming in on the neutral. Have you bonded the railing yet?Thank you for your knowledge and input, I greatly appreciate it. The meter and main panel butt right up against each other, no conduit. I was thinking about scheduling the power company to turn off the power to the house and removing everything coming into the panel from the meter. There aren't any battery backups in the house.
Unfortunately, I haven't been able to get my hands on a toner yet. I'll attempt to coordinate with someone to assist me while taking measurements while we disconnect and reconnect things. I certainly have a list of areas to look into. I'll keep everyone updated. Thank you again, for taking the time to help.The oscilloscope looks like it can do up to 100 MHz.
If you can get a toner to put a (<100MHz) signal on each suspect line, you should be able to see the signal on the oscilloscope when you tone the leaking line.
Did they lift the neutral in the meter?@JamesW Much appreciated!
Quick update: I had a power outage the other night 7/18 at 12:30 am. I ran out to the pool to take a voltage reading:
237 mV concrete to the railing
400 mV railing to the water
Power came back on within a couple of minutes by the time I got out there:
1.14 V concrete to the railing
1.57 V railing to the water
This was a random power outage. Unfortunately, I've been inundated with other work and haven't had a chance to plan a time to get the neutral off the meter.Did they lift the neutral in the meter?
it just means that it still could be coming in on the service as the cause of the stray voltage could have lost power also.This was a random power outage. Unfortunately, I've been inundated with other work and haven't had a chance to plan a time to get the neutral off the meter.
Here you say "main breaker to the house turned off." Is that from the power company or the solar panels?We have solar panels on the house. We had them come out to verify that there isn't a voltage leak or grounding issue on their equipment. With all of their equipment unplugged, power off, main breaker to the house turned off
If it is coming in on the neutral, what are the possible causes and fixes?Did they lift the neutral in the meter?